I'm doing an experiment with an UPS and lightbulb ...

I have a 1000VA UPS and a 15watt energy saver light bulb. I would like to know how long 'theoretically' I can get it to run for.

Also if I connect 2 x 15W bulbs .. will it be exactly half the time ?

Txs

0
Comment
Question by:Pete2003
7 Comments
 
LVL 6

Expert Comment

by:gjohnson99
ID: 12351038
If your UPS is 1000 va  

1000/ 15 = 66.6 hours

- 50 %  for advertising

likely  33.3 hour
 
2  15 watt bubs =  .5 x 33.3
0
 
LVL 8

Expert Comment

by:RLGSC
ID: 12351095
Pete2003,

Remember, the rating of a UPS typically is using a fairly new set of batteries. If you are planning for operational requirements, be VERY conservative (at least a factor of 2, possibly more) in terms of your safety factor. Old batteries have lower performance than a fresh set of batteries.

I hope that the above is helpful.

- Bob (aka RLGSC)
0
 
LVL 69

Expert Comment

by:Callandor
ID: 12351102
You need the conversion factor of 0.7 to translate 1000VA into 700watts.  The run time can be calculated by looking at MikProg's answer (the accepted answer) here: http://www.experts-exchange.com/Hardware/Q_21045370.html
0
U.S. Department of Agriculture and Acronis Access

With the new era of mobile computing, smartphones and tablets, wireless communications and cloud services, the USDA sought to take advantage of a mobilized workforce and the blurring lines between personal and corporate computing resources.

 

Author Comment

by:Pete2003
ID: 12366813
33 hours seems a bit much gjohnson99
RLGSC, the UPS is fairly new
That link is dead Callandor
0
 
LVL 69

Accepted Solution

by:
Callandor earned 300 total points
ID: 12368887
I just tried it and it worked.  Here's the gist.

MikProg said:

"Power consumption calculation is simple. Take a sum of numbers signed on  every power supplay in your servers. And calculate VA as reverse Callandor (thanks) formula. I.e.
    (400+500+450+...)/0.7
It will garantee that maximum computer consumption does not affect your UPS. UPS will not crush, not burn out if power consumption larger than maximum allowed. Simply power quality will lower. It is really bad for your servers too.

Why VA is used for UPS instead of W for power supplay. UPS must hold power until servers becomes down. It is easyer to calulate time using VA. Example: UPS 2200 VA with 2 AH (amper-hour) capacity. 220 V out.

2200 VA / 220 V = 10 A

60 minutes * 2 AH / 10 A = 12 minutes  UPS will hold 10A power at 220 V

If power consumptions is less then 10 A for example 5 A time will be not 24 minutes but slightly more about 26-27 min.
Taking total servers power and down time as target you can calculate parameters of new UPS. Usually manufacturers are publish power in VA and offline work time. The parameters you really need is UPS VA and battary AH. Serious manufacturers are always publish them. The only thing you need is check if UPS maximum allowed current is less then possible consumption it is
  UPSmac A > (400+500+450+...)/0.7/220 A"
0
 

Author Comment

by:Pete2003
ID: 12369007
I'm not sure where you got the 60 minutes from ?

also where do you get the amp rating for the UPS ...

Here is the UPS link http://www.cellpower.com.tw/main3.html (the 1000VA UPS)

and the bulb is still a 220V (15Watt) energy saver light bulb
0
 
LVL 69

Expert Comment

by:Callandor
ID: 12372948
The 60 minutes is to convert from ampere-hours to ampere-minutes, and finally minutes.  You need to know the current capacity of your UPS (the example above is 2AH, but yours may be different); as MikProg said, the better models have this specification on the label.

Your calculation would be 1000VA / 220V = 4.545 amps, so whatever the current capacity is divided by 4.545 would give you the run time in hours at full power.  Multiply by 60 to get it in minutes; if using less current, your run time will be longer.
0

Featured Post

Live: Real-Time Solutions, Start Here

Receive instant 1:1 support from technology experts, using our real-time conversation and whiteboard interface. Your first 5 minutes are always free.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Suggested Solutions

Every server (virtual or physical) needs a console: and the console can be provided through hardware directly connected, software for remote connections, local connections, through a KVM, etc. This document explains the different types of consol…
What do we know about Legacy Video Conferencing? - Full IT support needed! - Complicated systems at outrageous prices! - Intense training required! Highfive believes we need to embrace a new alternative.
Two types of users will appreciate AOMEI Backupper Pro: 1 - Those with PCIe drives (and haven't found cloning software that works on them). 2 - Those who want a fast clone of their boot drive (no re-boots needed) and it can clone your drive wh…
With Secure Portal Encryption, the recipient is sent a link to their email address directing them to the email laundry delivery page. From there, the recipient will be required to enter a user name and password to enter the page. Once the recipient …

785 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question