What is the average or typical heat in btu's put out by a 3/4 full 84" rack?

My company is moving to a custom built office.  I was asked to figure out in BTU's, what kind of heat each rack would put out, or a pretty close guess, for cooling purposes.  Our 5 racks (enclosed) are 3/4 full now, with 1u servers, and a 3com switch, along with a couple of 16 disk arrays.  The booklet that came with the server says it puts out about 1372 BTU an hour.  We will probably be adding more servers later.  So, I am guessing 40, 000 btu per hour, per rack(27 servers, and switches, ups, etc.).  That just doesn't sound right, does it? I am guessing the 1372 is server at full load?  That just sounds awful high.  In 6 yrs in IT, sadly, this is the first time I have been asked this.  
dfridgeAsked:
Who is Participating?

[Product update] Infrastructure Analysis Tool is now available with Business Accounts.Learn More

x
I wear a lot of hats...

"The solutions and answers provided on Experts Exchange have been extremely helpful to me over the last few years. I wear a lot of hats - Developer, Database Administrator, Help Desk, etc., so I know a lot of things but not a lot about one thing. Experts Exchange gives me answers from people who do know a lot about one thing, in a easy to use platform." -Todd S.

CallandorCommented:
1372 BTU equals 402 watts/hour, which is a pretty reasonable power consumption if it's running at full load.  All the elctricity consumed has to turn up somewhere, and in this case it is in the form of heat.  You can check each server for their rated power consumption, but actual use will be much less (you never run a computer at the maximum power supply rating), and a tool like a Kill-A-Watt device will tell you what it is actually using.

Experts Exchange Solution brought to you by

Your issues matter to us.

Facing a tech roadblock? Get the help and guidance you need from experienced professionals who care. Ask your question anytime, anywhere, with no hassle.

Start your 7-day free trial
computerfixinsCommented:
We use the 1-ton of cooling per rack in our data center...just as a generelized rule of thumb...  

The lazy admin way :)

that said; you should probaly use callandor's... o.O

It's more than this solution.Get answers and train to solve all your tech problems - anytime, anywhere.Try it for free Edge Out The Competitionfor your dream job with proven skills and certifications.Get started today Stand Outas the employee with proven skills.Start learning today for free Move Your Career Forwardwith certification training in the latest technologies.Start your trial today