hi a circut tripped last night and the servers were down this morning. Do the power chute ups batteries that are attached to our two servers shutdown the servers or are they just there to give you a bit of time to physically shutdown the servers.
I was wondering this as what i was told about ups's is that they provide you with a time frame within which you can shutdown the servers in the correct manner
Comment
Watch Question

Lee W, MVPTechnology and Business Process Advisor
CERTIFIED EXPERT
Most Valuable Expert 2013
Commented:
If they are connected to the servers with data cables, then you can configure the servers to shutdown.  So if you have them connected and the software configured, yes, they will automatically shut down the servers.

Not the solution you were looking for? Getting a personalized solution is easy.

Ask the Experts
Guy Hengel [angelIII / a3]Billing Engineer
CERTIFIED EXPERT
Most Valuable Expert 2014
Top Expert 2009
Commented:
ups usually do not shutdown the servers automatically, but:
* if you have a ups connection and drivers installed, the servers could shutdown by request of the ups.
* if the ups power is fully used, the servers will switch off, missing power (this is like a delayed power failure)

Usually, the second case is what happens, you have to check how much power your ups can give you vs how much power your servers, monitors etc use.
Commented:
ups provide power backup for some time it depends on ups and the load factor, usually 10 to 15 minutes or it sets on battries condition i mean if battries drained 60% or what ever they set shutdown the ups so when ups shuts down the systems also. if u have installed a card which i think called snmp card which have an ethernet port or serial cables which connected to your server, install and configure appropriate software then if can be configure that ups sends shutdown signals to your systems and they shutdown normal before ups batteries drained and it stops suppliying power.
the servers remain shutdown not restart even after power restores is depends on bios settings.
CERTIFIED EXPERT
Commented:
I use APC UPS's I have installed the Powerchute app on my main server and when there are only 5 mintues remaining the powerchute app will shutdown windows before it runs out of power. the only problem is that you  can only allow one pc per APC device (i only purchase the same model so i dont know if they have one that can support multile clients)...

Note not all products have that feature..

If you have powerchut software installed then open it and go to configuration then runtime then you should be able to see if the option
keep my computer running for as long as ##. if that option is check then the server will shutdown on ## minutes
A correctly specified and installed UPS will shut down a server when remaining battery capacity falls to aprox. 10 or 20%.
Without a shutdown signal from the UPS, the server cannot shutdown safely before battery exhaustion, and there is a strong risk of loosing data when the server is finally "dropped".

Your UPS may have a serial data cable connected to a comx: port on the server, in which case is probably uses shutdown. APC's often have management software (powerchute)to view UPS stats, and perform tests, look for this.

Newer UPS's such as the MGE Evolution can send shutdown signals to muliple servers on the LAN, and are a good choice when protecting multiple servers from one UPS.
Commented:
You should also be able to configure the PowerChute app to restart the servers, after power is restored and stabilized for X minutes.

Author

Commented:
sorry for the delay in getting back
thanks for the info very useful
Access more of Experts Exchange with a free account
Thanks for using Experts Exchange.

Create a free account to continue.

Limited access with a free account allows you to:

  • View three pieces of content (articles, solutions, posts, and videos)
  • Ask the experts questions (counted toward content limit)
  • Customize your dashboard and profile

*This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.

OR

Please enter a first name

Please enter a last name

8+ characters (letters, numbers, and a symbol)

By clicking, you agree to the Terms of Use and Privacy Policy.