I am calculating BTU of air conditioner for our server room. There are 30+ servers in the server room. Most of them have redudant power supply. For example, if a Dell 2950 server has 2 x 700 W power supply (from server specifications), how much watt of this server need? Do I need to consider peek time or running time?

Thanks,
vijitcAsked:
Who is Participating?
I wear a lot of hats...

"The solutions and answers provided on Experts Exchange have been extremely helpful to me over the last few years. I wear a lot of hats - Developer, Database Administrator, Help Desk, etc., so I know a lot of things but not a lot about one thing. Experts Exchange gives me answers from people who do know a lot about one thing, in a easy to use platform." -Todd S.

michkoCommented:
0
jamietonerCommented:
If they are all dells (or you have the btu and power info from the non-dell devices) you can use dell's rack advisor program to calculate btus and max power usage.
http://support.us.dell.com/support/downloads/download.aspx?c=us&cs=04&l=en&s=bsd&releaseid=R91359&formatcnt=1&libid=0&fileid=119636 
0

Experts Exchange Solution brought to you by

Your issues matter to us.

Facing a tech roadblock? Get the help and guidance you need from experienced professionals who care. Ask your question anytime, anywhere, with no hassle.

Start your 7-day free trial
nobusCommented:
you can try to calculate thepower needed for each server  here :
http://extreme.outervision.com/psucalculator.jsp      
or use  a watt meter, to measure each one's power consumption :
      http://www.the-gadgeteer.com/review/kill_a_watt_electric_usage_monitor_review
0
CompTIA Security+

Learn the essential functions of CompTIA Security+, which establishes the core knowledge required of any cybersecurity role and leads professionals into intermediate-level cybersecurity jobs.

vijitcAuthor Commented:
What could be real power consumption if I have 2 x 700W deduandant power supplies running? How can I find that?
0
michkoCommented:
APC while paper for calculating total cooling requirements of your data center:
http://www.apcmedia.com/salestools/NRAN-5TE6HE_R1_EN.pdf
0
nobusCommented:
you cannot calculate it starting from the power supply - that is only max power that you can use.
0
It's more than this solution.Get answers and train to solve all your tech problems - anytime, anywhere.Try it for free Edge Out The Competitionfor your dream job with proven skills and certifications.Get started today Stand Outas the employee with proven skills.Start learning today for free Move Your Career Forwardwith certification training in the latest technologies.Start your trial today