UPS died and wont turn on.

mark_06
mark_06 asked
on
Medium Priority
605 Views
Last Modified: 2013-12-11
HI,

I am running a Sola UPS 520RM 1050. Last night it just turned itself off and it wont come back on. When I press the power button it appears to be turning on and within 5 seconds it turns itself off again. However during these 5 seconds it doesnt output any power.
The UPS is about 5 years old, so I am thinking it could be the battery, however I dont know much about UPS's so I was wondering if someone could tell me what the possible causes could be.

Thanks

Mark
Comment
Watch Question

Cloud/Infrastructure Solutions Architect
CERTIFIED EXPERT
Commented:
When you press the button and for the 5 secs, it sounds like its trying to apply power to the battery but failing. Sounds like the UPS battery has taken the dive.
Sola was bought by Powerware.

They have software, Sola - Commander Pro, that you may be able to install to diagnose the UPS through the RS-232 port:

http://www.powerware.com/Software/Downloads.asp#leg

Click the "Sola - Commander Pro" link.
By the way, battery life is typically 3 years, so you may just want to replace it considering it's obsolete too. The cost for new batteries is typically 90% of the cost of a new UPS anyway...