Powerchute will not recognize other devices

Posted on 2008-06-17
4
1,921 Views
Last Modified: 2010-04-21
I have installed an APC3000 Smart-UPS.
It came with Powerchute Business Edition Basic.
I have 3 Windows 2003 servers attached to this UPS.

The instructions say to install the Agent on each device plugged into(electrically) the UPS (up to 5).  However, during the installation, it does a search for which COM port UPS is attached to....No problem for the computer which is directly attached via serial cable.  However, when I went to install it on the other devices, the installation did not want to continue if it couldn't find the COM port.

I attempted to bypass this problem, by moving the serial cable to the next computer I installed the agent on, and did the same for the third. Then, I installed the Powerchute Server software on one of the servers.

I was able to get the Powerchute device list to discover the the computer directly connected to the UPS.  However, my bypass must not have been the right answer, because I can't get it to find the other two computers which are plugged in (electrically) but have no communication port attached to the UPS. All these computers are on the same network segment (172.20.20.x).  

Does anyone know how this software talks to all the machines the agent is installed on?
0
Comment
Question by:kolson14
  • 2
  • 2
4 Comments
 
LVL 18

Expert Comment

by:Don S.
ID: 21809488
You would need an interface expansion card in the SmartUPS and communications cable to each of the computers.  No communication cable = no communication that the UPS is on battery = no ability to gracefully shut down the server.

The part number for the card and two cables is: AP9607CB
0
 
LVL 1

Author Comment

by:kolson14
ID: 21809647
Thank you so much for that.  I also really appreciate the part number!  You Rock!

If what you are saying is correct, then why does a company like APC not include this information in their instruction guides? Their hardware installation makes no mention of expansion cards.  If you are allowed up to 5 devices with one UPS, but initially they will only give you enough cables and connections to support one, then they should give you the tools or information about those tools so those 5 devices can be hooked up.  

This is why I just can't help but wonder if there's another answer.  I understand the communication cable, but wouldn't the fact that all the machines are networked play some part in this?  

Sorry to doubt you, but I just feel like there's something missing.  However, if you are right....then APC needs to get on the ball and cater to us beginners a bit more!
0
 
LVL 18

Accepted Solution

by:
Don S. earned 50 total points
ID: 21848102
The software you are given free with the UPS is limited to monitoring five devices.  Their pro version which costs $ is unlimited.
Think about it, how would the mesage that the UPS is on battery get to a computer if there was no signal cable between the two?  There is no such thing as a computer power supply that reads signals from the power cord and the UPS doesn't put signals on it's power output.  As for the computers being networked, how would one computer know what it is plugged into?  If it doesn't know what it is plugged into, how would it know that it is about to lose power unless it got a signal from it's power source?
0
 
LVL 1

Author Closing Comment

by:kolson14
ID: 31468177
I may have not been what I wanted to hear, but it made sense.
0

Featured Post

Networking for the Cloud Era

Join Microsoft and Riverbed for a discussion and demonstration of enhancements to SteelConnect:
-One-click orchestration and cloud connectivity in Azure environments
-Tight integration of SD-WAN and WAN optimization capabilities
-Scalability and resiliency equal to a data center

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Suggested Solutions

Title # Comments Views Activity
Wired Network vs Wireless 12 66
No Wireless Networks Visible In Windows 10 7 77
VMware ESXi vswitch - performance question 2 77
Internet link load balancer 6 67
In this article, I am going to show you how to simulate a multi-site Lab environment on a single Hyper-V host. I use this method successfully in my own lab to simulate three fully routed global AD Sites on a Windows 10 Hyper-V host.
For many of us, the  holiday season kindles the natural urge to give back to our friends, family members and communities. While it's easy for friends to notice the impact of such deeds, understanding the contributions of businesses and enterprises i…
This video gives you a great overview about bandwidth monitoring with SNMP and WMI with our network monitoring solution PRTG Network Monitor (https://www.paessler.com/prtg). If you're looking for how to monitor bandwidth using netflow or packet s…
In this tutorial you'll learn about bandwidth monitoring with flows and packet sniffing with our network monitoring solution PRTG Network Monitor (https://www.paessler.com/prtg). If you're interested in additional methods for monitoring bandwidt…

830 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question