Symmetra LX 1600 rm shuts down everything

I was testing my Symmetra LX 1600 rm and all seemed to be running fine.  But after about 15 minutes the Symmetra LX 1600 rm tripped all of the servers and shutdown power to the outlets.  I cannot find any setting for this on the configuration. The front counter still had over 1.5 hours left of run time...
0
burstadmin
Asked:
burstadmin
  • 2
  • 2
1 Solution
 
PCBONEZCommented:
I've looked at the specs and I think what you had left was 1.5 minutes, not hours.
0
 
burstadminAuthor Commented:
No, it was hours.  I reset the system and I am running another test today.  
0
 
PCBONEZCommented:
Hours you say.
That's interesting because APC gives the backup time at 16.9 minutes at 50% load.

0
 
burstadminAuthor Commented:
no, I have 1.35 hours of runtime on this unit with the five expansion cab's.  I found the solution, it is a check box that says shotdown the UPS after server shutdown.  