Trying to determine if my power infrastructure can accomadate a new blade enclosure

Hello,
We have a Symmetra PX 20kW UPS in our data center. I am trying to determine whether or not it can provide the required power for a HP BladeSystem c7000 Enclosure. Currently the UPS shows a load of 63%. Please let me know if you need more information. I'm not sure how to calculate this ? Thanks in advance.
Avatar of jbristle
jbristle

Offhand, I would say no if you want a run time of more than a few minutes at peaks.
It really depends on how many blades, and which type, and the power supply configuration.

What is the input voltage and phase of the UPS?

Your currently at 63%, which should be around 12.5kW. If you have a full blade chassis, you could possibly peak at ad additional 14.4kW if you have high temp's, high cpu utilization, high i/o etc..

If you plan on growing the blade center incrementally, and you start out small, you will probably be fine for a while.

Avatar of chaz21

ASKER

the input voltage is 208V 3-Phase

from there we deliver power to the racks using switched rack pdus @ 120V single-phase

the blade enclosure we are looking at is the HP BL c7000 CTO.

the power supply type listed on hp's website is a 2400W high efficiency power supply. the enclosure would use 6 power supplies (single phase IEC-320 C20 @  

our goal is to consolidate about 25 physical servers to the blade enclosure using vmware. we would have to power the blade enclosure and the servers that will be replaced during the p2v (physical to virtual) conversion.

my thinking is that once we have all of the old hardware converted to virtual running on the blade we should be ok ?

thanks for the insight, really appreciate it.
As long as you decommission servers as you bring up blades and keep your power balanced, you should be good, just make sure monitor your UPS load, and keep your essential servers on the UPS. If your budget allows, you might want to expand that UPS to 40kW.
Avatar of OriNetworks
jbristle has a good suggestion but it sounds like you want all of it running at the same time. Would it be at all possible to borrow or rent an additional UPS and power from somewhere until you can decomission the old servers?
Avatar of chaz21

ASKER

our frame is actually maxed out at 20kW, their is no room for expansion so unfortunately that's not an option. there's a total of 3 power modules @ 10kW each with two being active and one acting as spare.

we do have some old APC equipment lying around, however, source power comes into the data center straight to the symmetra. i'm not sure how we could utilize the old equipment without source power ?

jbristle,  can you explain how you came up with 14.4kW for the blade enclosure ? it would be greatly appreciated. thanks again for all this great information. to a novice data center administrator its quite helpful!
ASKER CERTIFIED SOLUTION
Avatar of jbristle
jbristle

Link to home
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
Start Free Trial
This is a great section of the APC site for gathering this kind of information.  There are selectors for multiple aspects of your business.  You can usually build these to very closely fit your specific situation.

http://www.apc.com/sizing/selectors.cfm

Avatar of chaz21

ASKER

this is actually our exact model:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ISX20K20F

i had to call apc to get that link b/c i couldn't find it anywhere on there website either. so we are indeed maxed out.  there is an option to run all 3 modules at once so 30 kW but then we wouldn't have redundancy which to me wouldn't make a whole lot of sense.

i doubt that we would want to add an additional unit as the investment for this project (blade enclosure, vmware licenses, and shared storage) is already pretty high up there.

based on these numbers:
20kW max capacity
12.5kW already being used
and the blade enclosure requiring at least 7.2kW

i don't see how our current infrastructure would be able to handle the load.  would you guys agree ??




You could give it a bump to 30kW for a short period while migrating the servers. But if you have any concern for redundancy, I would not.

Considering the cost of the new blade center, I would try to get funding for a new UPS also and have a talk with your electrician about bringing in some more circuits.