calculating amps * volts on dell poweredge 2950

Posted on 2009-06-26
4
Medium Priority
?
9,066 Views
Last Modified: 2013-12-11
Hello guys and as always thanks for your time and expertise.
We have a Dell Poweredge 2950 and I need to calculate the power requirements for a ups.  We're going to connect five of these servers into a ups.
On the power supply for the server - here's the info listed:
Input 100-240v
50/60 H
Max AC Current 9.3AMP
Output +12v 62.4amp
+3.3usb 3.8amp
Total output power not to exceed 750 watts
- Now I haven't done this in a while but I thought the calculation was amps * volts.  With that being said, am I using the 9.3 amps in my calculation.  I would appreciate any help on this.  Thanks.
0
Comment
Question by:pendal1
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
4 Comments
 
LVL 2

Assisted Solution

by:chronosyu
chronosyu earned 660 total points
ID: 24725890
Hi, i thionk this page will hlep you a lot, take a look. let me know

http://bugclub.org/beginners/miscellaneous/upscalc.html
0
 

Assisted Solution

by:willsorrell
willsorrell earned 660 total points
ID: 24726400
You are not going to get a true picture of how much power your servers draw by looking at the tag on the power supply.  You've got a couple of better options:

1 - Go to a UPS manufacturer's website (like www.apc.com) and use their selector tool.  This will ask you for input on the model, processor, number and type of drives, etc.
2 - Purchase a tool like the "Kill-a-Watt" from p3International and measure the power draw directly.  I bought mine at Harbor Freight Tools for $40.  This is really simple - you power down the equipment, unplug it from the wall, plu the "Kill-a-watt" device in the wall, and then plug your equipment into the Kill-a-watt.  Depending on the total draw (check the rating) you could just plug a power strip into the Kill-a-watt and then put all your equipment on the power strip and measure it all at once.

What I found is that everyone, especially the folks trying to sell you a UPS unit, will dramatically overstate the power draw of your equipment.  Who knows why (liability, greed, whatver).

The formula for Watts in a standard electrical device (light bulb, hair dryer, etc.) is Volts times Amps, but electronic equipment like servers have what is known as a Power Factor, which actually reduces the total draw.  So for a hairdryer, 1850VA = 1850 watts, but for a server 1850VA might only be 1200watts (and that would be one hell of a big server, illustration purposes only).  That's why you should always consider the watts you need, not the volt amps.  Manufacturers like APC and Tripplite always use VA as their "marketing measurement" but when you dig into the details, you'll see that a 1500VA UPS might only be rated for 1200 watts, or even 1050.

So the simple way to do it is use APC or similar to estimate the watt draw of your equipment and size the UPS accordingly.  The other, more accurate (and fun) way, is to buy a tool and watch the draw in real time.

There are other considerations too, like "line-interactive" vs. "double online conversion" UPS. but that's a little esoteric and probably not something to worry too much about unless you are going to get over 5KVA.  I'm sure APC and Tripplite would love to argue the relative merits of the technologies, but all you really want is battery-backup for your two servers.

Another consideration is extended run time.  Vendors usually sell two different models of same size units - one capable of daisy-chaining additional battery and one not.  If you want to have any kind of extended run time (more than just graceful shutdown time) you should look into this as well.

Hope that helps.
0
 
LVL 10

Accepted Solution

by:
dnilson earned 680 total points
ID: 24726617
WHile I agree that an actual measurement or a UPS manufacturesr calculator is a better way to go, you question was to formula.

9.3 amps time 120 volts = 1116 VA.  This doesnt have to be discounted by the sine factor (0.707) because current was already defined as AC current.

750 / 1116 = .67 (67%) a respectable and believable conversion factor for a switching power supply.

The UPS Will have a MAX impress load of (approx) 1116 VA, and an average dependant upon installed hardware, speed, ambient tenperature, etc.

===============================
ANother thing to take into consideration is the effect of the dual redundnat power supplies.  In my measurements, having BOTH supplies powered draws 1-1.5 amps LESS than having either one powered, or in worst case terms, apower supply failure generates a n approxc 1.5 amp step function increase on the opposite bus.  Both continous capacity (the VA ratign o nthe box) and the intantaneous surege capacity (a function of the UPS to supply constant voltage depite astep load) which is a spec ofeten more deeply buried.


lots of little peices to look at ......

0
 

Author Closing Comment

by:pendal1
ID: 31597072
Guys - thanks for the great input.  Very helpful and informative.  Much appreciated.
0

Featured Post

Plug and play, no additional software required!

The ATEN UE3310 USB3.1 Gen1 Extender Cable allows users to extend the distance between the computer and USB devices up to 10 m (33 ft). The UE3310 is a high-quality, cost-effective solution for professional environments such as hospitals, factories and business facilities.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Learn how the use of a bunch of disparate tools requiring a lot of manual attention led to a series of unfortunate backup events for one company.
Many businesses neglect disaster recovery and treat it as an after-thought. I can tell you first hand that data will be lost, hard drives die, servers will be hacked, and careless (or malicious) employees can ruin your data.
In this Micro Tutorial viewers will learn how to use Windows Server Backup to create full image of their system. Tutorial shows how to install Windows Server Backup Feature on Windows 2012R2 and how to configure scheduled Bare Metal Recovery backup.…
This tutorial will walk an individual through setting the global and backup job media overwrite and protection periods in Backup Exec 2012. Log onto the Backup Exec Central Administration Server. Examine the services. If all or most of them are stop…

719 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question