Installing Smart UPS 1500 on 2003 server

Posted on 2009-07-06
3
1,150 Views
Last Modified: 2013-12-11
I have an old 1400 ups using Power Chute Pro 2000 running on a server 2003. I am installing the APC 1500 Smart UPS on the same server. Since I am no expert installing an ups and configuring the software I need to know.

If I should uninstall the older software first then down the server then replace the UPS then boot and install the Power Chute Business Edition Basic onto the server.

Or uninstall the old software and then install the new Power Chute and then down the server and replace the Hardware. (I guess there is no chance that I can just swap out the UPS and use the older software and expect everything to work)

The only hardware running on the UPS is the server and a Switch. The old system is using the RS232 connector. I intend to use the same. I am trying to do this the quickest and most simple way. I don't need to monitor the software, just to configure it on the server to shut down in case of a power outage; shut down and boot back up into saved settings in the system state&

Any expert help is greatly appreciated!!
Thanks!


I have added high points because this is important for me to get right the first time.
0
Comment
Question by:ralraus
3 Comments
 
LVL 8

Accepted Solution

by:
Pete_Zed earned 500 total points
ID: 24791297
The approach I would take would be:

Uninstall the old software. But first, make a note of any special settings you have in the old software so you can be assured that it will perform the same way in the new software

Shut down the server and replace the UPS

Start the server and install the new software and configure
0
 
LVL 2

Expert Comment

by:cirlare
ID: 24792207
if i was you i would of remove the data cable between ups and server first, uninstall software. reboot server, install new software and then shut down and install new ups.

0
 

Author Closing Comment

by:ralraus
ID: 31600463
Thanks for the help. I was on it early this am. Everything worked out great, had an issue with the unix server running on the same UPS but using different software, which is a issue I am working on with DDS; if they would let me use power chute it would be easier. The Win2003 server and ups are in an auto dealership so I needed to be absolutly sure it worked the first time. Thanks
0

Featured Post

Optimizing Cloud Backup for Low Bandwidth

With cloud storage prices going down a growing number of SMBs start to use it for backup storage. Unfortunately, business data volume rarely fits the average Internet speed. This article provides an overview of main Internet speed challenges and reveals backup best practices.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Back in July, I blogged about how Microsoft's new server pricing model, combined with the end of the Small Business Server package, would result in significant cost increases for many small businesses (see SBS End of Life: Microsoft Punishes Small B…
ADCs have gained traction within the last decade, largely due to increased demand for legacy load balancing appliances to handle more advanced application delivery requirements and improve application performance.
This Micro Tutorial will give you a basic overview how to record your screen with Microsoft Expression Encoder. This program is still free and open for the public to download. This will be demonstrated using Microsoft Expression Encoder 4.
With the power of JIRA, there's an unlimited number of ways you can customize it, use it and benefit from it. With that in mind, there's bound to be things that I wasn't able to cover in this course. With this summary we'll look at some places to go…

867 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question

Need Help in Real-Time?

Connect with top rated Experts

21 Experts available now in Live!

Get 1:1 Help Now