Solved

UPS reports overvoltage - should I be concerned?

Posted on 2010-11-29
6
Medium Priority
?
1,119 Views
Last Modified: 2012-05-10
I have an APC Smart-UPS supplying an SBS server. The PowerChute software has thrown up the error "The UPS has experienced a high input voltage more frequently than normal".

The electrical spur supplying the UPS is new, installed last week.

Looking at the graph in the PowerChute console for the last 24hrs, the input voltage has mostly been between 249 and 252 with a single spike of 255. In the last few hours, it's fallen to between 240 and 243 (The domestic supply in the UK is 240V).

I know how to increase the High Voltage limit from it's current limit of 253V, but I'm not sure whether that would be just ignoring the problem.

Should be concerned about the quality of the electrical supply? And is there any risk to the server?
0
Comment
Question by:andymilli
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
  • 2
  • 2
  • 2
6 Comments
 
LVL 30

Accepted Solution

by:
Britt Thompson earned 1400 total points
ID: 34229134
Since you're using a Smart-UPS your server is OK...that "Smart-UPS" means it filters the dirty power and makes it safe for the server. I would consult and electrician to make sure your circuits are wired correctly and your fuses are not in need of replacement.
0
 

Author Comment

by:andymilli
ID: 34229284
Thanks, I thought that would probably be the case, but I don't like guessing when it comes to a server!

I've spoken to the electrician who installed the new spur last week, but he doesn't think we should be too concerned. As the spur and fuse are both brand new, he thinks the problem is with the supply into the building, and if we continue to get high voltages we should perhaps contact the electricity supplier.
0
 
LVL 30

Expert Comment

by:Britt Thompson
ID: 34230431
Over voltage can ruin your equipment so I'd be sure you have a Smart-UPS for just about everything...I know in the US we can get surge protection at the source where the power comes into the building to eliminate the need for the more expensive UPS devices and surge protectors.
0
Building an interactive eFuture classroom

Watch and learn how ATEN provided a total control system solution including seamless switching matrix switch, HDBaseT extenders, PDU, lighting control to build an interactive eFuture classroom.

 
LVL 32

Expert Comment

by:aleghart
ID: 34235605
255VAC shouldn't worry you.  Even in "standard" mode, it will take up to 285VAC.  I'd leave it as-is and compare with other UPS.  Do you have others that are also 230V?


==

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA3000I

Input voltage range for main operations
160 - 285V

Input voltage adjustable range for mains operation
151 - 302V
0
 

Author Comment

by:andymilli
ID: 34247404
Thanks. It's small network and this is the only UPS we have, with two servers running of it. We have a couple of Linux servers with surge protectors, but they aren't used much and are not critical. Could this be a risk for routers and switches?
0
 
LVL 32

Assisted Solution

by:aleghart
aleghart earned 600 total points
ID: 34252468
Power quality is always a risk factor.  Most power supplies will have a range for acceptable voltage, as you can see by the spec on your UPS.  Computer power supplies are also a bit flexible.  Network gear is also a little flexible.  Nobody gets exactly 120V on "120" service.  At the very minimum I'd put a power conditioner in place.  It will trim excess voltage and boost low voltage, even surviving through very short dips that would otherwise crash a system.  They're cheap (50-75 USD), and can handle up to 1000W or more of load.
0

Featured Post

On Demand Webinar: Networking for the Cloud Era

Did you know SD-WANs can improve network connectivity? Check out this webinar to learn how an SD-WAN simplified, one-click tool can help you migrate and manage data in the cloud.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

The 6120xp switches seem to have a bug when you create a fiber port channel when you have a UCS fabric interconnects talking to them.  If you follow the Cisco guide for the UCS, the FC Port channel will never come up and it will say that there are n…
INTRODUCTION The purpose of this document is to demonstrate the Installation and configuration, of the HP EVA 4400 SAN Storage. The name , IP and the WWN ID’s used here are not the real ones. ABOUT THE STORAGE For most of you reading this, you …
In this video, Percona Director of Solution Engineering Jon Tobin discusses the function and features of Percona Server for MongoDB. How Percona can help Percona can help you determine if Percona Server for MongoDB is the right solution for …
In this video, Percona Solutions Engineer Barrett Chambers discusses some of the basic syntax differences between MySQL and MongoDB. To learn more check out our webinar on MongoDB administration for MySQL DBA: https://www.percona.com/resources/we…

688 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question