what's the best temperature to keep a server room at? I'm involved in a little debate over that. thanks.
0
Comment
Question by:knfitz
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
5 Comments
 
LVL 7

Accepted Solution

by:
XLITS earned 500 total points
ID: 34953946
We have always kept our server room at 65 degrees and it seems to be fine.  This has been our policy for the past 10 years and haven't had any issues relating to temperature.
0
 
LVL 3

Assisted Solution

by:KCarney81
KCarney81 earned 500 total points
ID: 34953966
60-65 usually does the trick
0
 
LVL 20

Assisted Solution

by:woolnoir
woolnoir earned 500 total points
ID: 34954055
65F +- about 5F it depends on your 'green' requirements as obviously a cooler temp uses more energy and has a bigger environmental impact (and cost).
0
 
LVL 11

Assisted Solution

by:David Kroll
David Kroll earned 500 total points
ID: 34954112
Ours is 68 and everything's fine.  Wouldn't mind being 65, but trying to reduce electrical usage.
0
 
LVL 44

Expert Comment

by:Amit
ID: 34954197
General recommendations suggest that you should not go below 10°C (50°F) or above 28°C (82°F). Although this seems a wide range these are the extremes and it is far more common to keep the ambient temperature around 20-21°C (68-71°F). For a variety of reasons this can sometimes be a tall order.

Temperature inside a rack is not to exceed 23°C or 73° F.

Another danger is humidity

Low relative humidity (as of 35% rH) has the danger of causing electrostatic discharge (ESD). ESD is caused by static charges resulting from people movement, charges on furniture etc... These charges are mostly not noticeable but when discharged to or in proximity of IT equipment, they can cause severe damage to the equipment.

Another danger of low humidity is the break down of some plastics in your equipment resulting in premature aging of it.

To overcome the danger of low humidity, moisture is often added to temperature controlling systems to avoid too dry conditions in server rooms.

High humidity or rapid temperature drops result in condensation that can occur on any surface. Water can condensate on the inside of IT equipment and cause rust or dust & dirt being deposited. This pose a great risk to the components and as a result to the availability of the equipment.

Relative Humidity (rH) is server rooms should be around 50% with a +/- 10% margin.
0

Featured Post

Plug and play, no additional software required!

The ATEN UE3310 USB3.1 Gen1 Extender Cable allows users to extend the distance between the computer and USB devices up to 10 m (33 ft). The UE3310 is a high-quality, cost-effective solution for professional environments such as hospitals, factories and business facilities.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

In this blog, we’ll look at how improvements to Percona XtraDB Cluster improved IST performance.
The top devops trends for 2017 are focused on improved deployment frequency, decreased lead time for change and decreased MTTR.
In this video, Percona Director of Solution Engineering Jon Tobin discusses the function and features of Percona Server for MongoDB. How Percona can help Percona can help you determine if Percona Server for MongoDB is the right solution for …
In this video, Percona Solutions Engineer Barrett Chambers discusses some of the basic syntax differences between MySQL and MongoDB. To learn more check out our webinar on MongoDB administration for MySQL DBA: https://www.percona.com/resources/we…
Suggested Courses

765 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question