I currently have an APC SmartUPS module RT6000 with four additional battery packs.  See URL below for reference.  I also currently own a Huskey 5000 watt generator.  The Huskey has a 120/240V 20 amp twist receptacle.  The APC plug has an R6-30 plug.  Assuming that the draw off of the UPS is no more than 20 amps - should there be any issue using an L6-30 to L6-20 adapter so that the generator could power the UPS in the event of a general power outage?  Thank you for any insight.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=surt6000rmxli

http://www.homedepot.com/buy/electrical/alternative-energy-solutions/husky/5000-watt-generator-with-subaru-engine-77110.html

http://www.powerfig.com/nema-l6-30p-to-nema-l6-20-250v-20a.aspx
0
Comment
Question by:amigan_99
  • 3
4 Comments
 
LVL 124

Accepted Solution

by:
Andrew Hancock (VMware vExpert / EE MVE^2) earned 2000 total points
ID: 35702568
Your power draw for this UPS and it's batteries is going to be at least 4,200 Watts, this is very close to 5000 Watt capacity of your generation.

At surge potential if all batteries our flat after a power outage, i.e. the in-rush current may well exceed your generators capacity.

It's very close.
0
 
LVL 124
ID: 35702580
I think if it was me, I would test and check the current draw with a clamp meter to check the maximum current draw from AC.

The potential unknown here, is the four additional battery packs.
0
 
LVL 1

Author Closing Comment

by:amigan_99
ID: 35702666
Excellent.  Thank you.  I will probably go with a 10KVA model instead - only about $1,000.
0
 
LVL 124
ID: 35702685
Yes, far better, I've seen the front panel of a diesel generator blown off, due to incorrect sizing!

(it never recovered!, requiring a crane, to crane in the new generator, and tree's to be cut down!).
0

Featured Post

Get your Disaster Recovery as a Service basics

Disaster Recovery as a Service is one go-to solution that revolutionizes DR planning. Implementing DRaaS could be an efficient process, easily accessible to non-DR experts. Learn about monitoring, testing, executing failovers and failbacks to ensure a "healthy" DR environment.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

WARNING:   If you follow the instructions here, you will wipe out your VTP and VLAN configurations.  Make sure you have backed up your switch!!! I recently had some issues with a few low-end Cisco routers (RV325) and I opened a case with Cisco TA…
This article is written by John Gates, CISSP. Gates, the SNUG President-Elect, currently holds the position of Manager of Information Systems at Lake Park High School in Roselle, Illinois.
After creating this article (http://www.experts-exchange.com/articles/23699/Setup-Mikrotik-routers-with-OSPF.html), I decided to make a video (no audio) to show you how to configure the routers and run some trace routes and pings between the 7 sites…
If you're a developer or IT admin, you’re probably tasked with managing multiple websites, servers, applications, and levels of security on a daily basis. While this can be extremely time consuming, it can also be frustrating when systems aren't wor…

809 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question