kVA power load of Proliant G7 & Oracle T3/M4000 servers : single & dual power input


Q1:
From the power meter on the MCB mounted the wall, when I power up one rack
that has 7 Proliant DL380 G7 servers, the power load increased by 1.2kVA for
the DC room.  Due to shortage of power points, only one input per server is
connected up with power cords.  Suppose I have enough power points & 
connect up both power inputs on each server, will this increase the kVA power
load or it will still be the same 1.2kVA total load for the that entire rack?

Q2:
Does anyone has any estimation of kVA power load per Oracle Sparc T3 server
(populated with 4 SCSI HDDs & 32GB RAM& both power inputs connected) ?
These are new servers which will be coming in but I need to do some planning

Q3:
Same question as Q2 above but for Oracle M4000 server
Server HardwareHardwareComponents

Avatar of undefined
Last Comment
Duncan Meyers

8/22/2022 - Mon
ASKER CERTIFIED SOLUTION
Duncan Meyers

Log in or sign up to see answer
Become an EE member today7-DAY FREE TRIAL
Members can start a 7-Day Free trial then enjoy unlimited access to the platform
Sign up - Free for 7 days
or
Learn why we charge membership fees
We get it - no one likes a content blocker. Take one extra minute and find out why we block content.
Not exactly the question you had in mind?
Sign up for an EE membership and get your own personalized solution. With an EE membership, you can ask unlimited troubleshooting, research, or opinion questions.
ask a question
sunhux

ASKER

Thanks.

proliant G7 is about 280 Watts

T3-2 with 4 HDDs & 32GB RAM works out to about 800 Watts
(sample power)

M4000 with 2x 300GB HDDs and 16x 8GB RAM works out to 1038 Watts
(sample power)


So can I say the kVA of T3-2 would be 2.86 times of DL380 G7
& M4000 wud be 3.7 time the kVA of G7?
sunhux

ASKER


http://ideasint.blogs.com/ideasinsights/2010/07/server-benchmark-analysis---proliant-dl3xx-amd-vs-intel.html

Link above gave Dl380 G7 at 439 Watts :

> The DL385 G7 recorded an average power consumption of 463.3 Watts,
> compared to 438.5 Watts in the DL380 G7

What I need to know next is whether my assumption that if a server has 2 times
the Watts of another server, does this mean the kVA would be double as well?
SOLUTION
Duncan Meyers

Log in or sign up to see answer
Become an EE member today7-DAY FREE TRIAL
Members can start a 7-Day Free trial then enjoy unlimited access to the platform
Sign up - Free for 7 days
or
Learn why we charge membership fees
We get it - no one likes a content blocker. Take one extra minute and find out why we block content.
Not exactly the question you had in mind?
Sign up for an EE membership and get your own personalized solution. With an EE membership, you can ask unlimited troubleshooting, research, or opinion questions.
ask a question
Duncan Meyers

For the purposes of your calculations, kVA = kW or 1 Watt = 1VA. VA is used for AC where current may lead or follow voltage.
Experts Exchange has (a) saved my job multiple times, (b) saved me hours, days, and even weeks of work, and often (c) makes me look like a superhero! This place is MAGIC!
Walt Forbes
sunhux

ASKER
ok
Duncan Meyers

Thanks! Glad I could help.