I have a situation where I am connecting a sensing device to the input of an 1762-IF4 non-isolated input card to a PLC. The output of the device is a voltage output, where the output varies from 1 to 5V based on a corresponding input. The output of the device is faily low impedance (2k ohms).  The card input is a fairly high impedance (200k ohms) which is measured at the differential inputs. The offset can reach up to 200mV, but diminishes once the output is above 50% of scale. The offset is still present even when the analog input module is removed from PLC power.

When the device is powered and not connected to th PLC no offset can be observed.
0
Comment
Question by:farcuri
1 Comment
 
LVL 31

Accepted Solution

by:
Dr. Klahn earned 2000 total points
ID: 36913843
It sounds like there may be an unexpected current leak through the input.  A miniscule current leak of 1 uA through a 200K input impedance would produce an offset of 0.2 V.

Try shunting the PLC input with a 220K resistor.  If a current leak is the problem, this should cause the unwanted voltage offset to fall to half its value, but should not affect the voltage component due to the relatively low impedance (2K) of the device output.

If this is correct, then shunting the PLC input with a moderate resistance of 20K should cut the unwanted offset by 90%, which might be good enough and would save extended investigation to determine the exact cause.
0

Featured Post

Reclaim your office - Try the MB 660 headset now!

High level of background noise often makes it difficult for employees to concentrate fully on their jobs – or to communicate clearly on calls. The MB 660 headset helps you create a disruption free workspace.  

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

pc, laptop  monitor connection configurations
This article shows how to use a free utility called 'Parkdale' to easily test the performance and benchmark any Hard Drive(s) installed in your computer. We also look at RAM Disks and their speed comparisons.
This video shows how to quickly and easily deploy an email signature for all users in Office 365 and prevent it from being added to replies and forwards. (the resulting signature is applied on the server level in Exchange Online) The email signat…
Exchange organizations may use the Journaling Agent of the Transport Service to archive messages going through Exchange. However, if the Transport Service is integrated with some email content management application (such as an anti-spam), the admin…
Suggested Courses

564 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question