On the photography is  ilustrated noise because of welding machine.
How can i do noise filter?

The  ampitude is ± 30 V  for rectifier voltage 24V in time period of 3 micro seconds.
The rectifier voltage curent max is 20A.
tiggraph.bmp
0
Comment
Question by:pr2501
  • 6
  • 5
  • 3
14 Comments
 
LVL 69

Expert Comment

by:Callandor
ID: 37709323
The best solution is to not be on the same power circuit as the welding machine.  You should be able to isolate it with a UPS.  If you want to build your own noise circuit, you should look for a low-pass filter design: http://www.allaboutcircuits.com/vol_2/chpt_8/2.html
0
 

Author Comment

by:pr2501
ID: 37709343
I had try by ups, but no help.

It is that noise is generated ower the cables on secondar part of rectifier.
0
 
LVL 69

Expert Comment

by:Callandor
ID: 37710495
Did the UPS that you used include line conditioning?  There are line conditioners used for audio applications: http://www.amazon.com/Furman-Standard-Conditioning-Outlets-Spacing/dp/B0014598WQ
0
Sign your company up to try the MB 660 headset now

Take control and stay focused in noisy open office environments with the MB 660. By reducing background noise, you can revitalize your office and improve concentration.

 
LVL 44

Expert Comment

by:Darr247
ID: 37711366
What's the source being monitored in that picture?
Possibly, shielding would be more efficient than filtering.

Or, if it's, e.g., warping a CRT display, changing to an LCD display would stop it.
0
 
LVL 69

Expert Comment

by:Callandor
ID: 37718101
You may want to read this paper on 24v noise sources and how to deal with them in Europe: http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/gmc-rm001_-en-p.pdf
0
 
LVL 44

Expert Comment

by:Darr247
ID: 37720659
According to the data sheet I found for the 6EP1 434-2BA00, its input is supposed to be 340V-550V (400V-500V on the label) 3-phase, 47-63Hz.
How are you putting a 230V UPS on the primary side of the rectifier?

Anyway...  disconnect the load wires from the output terminals, connect your scope to the output terminals, and watch while the welds occur.
If there's no noise then, you know it's being induced into the load wires.
In that case, shield the load wires and ground only 1 end of the shield.

If there's still noise at the terminals without the load wires connected, add filtering at the output.

edit: for filtering, I was going to suggest something like a 50V 1000uF 10,000 hour @105c electrolytic (~$30 each) across the output... but I see that Rockwell paper linked by Callandor recommends just a ceramic 50V 1uF such as
http://www.newark.com/vishay-sprague/2c20x7r105k050b/capacitor-ceramic-1uf-50v-x7r-radial/dp/66C6721 (10%) or http://www.newark.com/kemet/c330c105j5r5ta/capacitor-ceramic-1uf-50v-x7r-radial/dp/72K6453 (5%) across the output (grounded common), or one of those from each side of the output to ground (ungrounded systems).
0
 

Author Comment

by:pr2501
ID: 37736877
Ok, i will be more professional now:
I have used sheme with elements (pictures), but no help:
problem from the picture still persist.
What must i do?
IMG-3595.jpg
IMG-3596.jpg
IMG-3598.jpg
IMG-3599.jpg
IMG-3600.jpg
0
 
LVL 44

Expert Comment

by:Darr247
ID: 37738360
As I said, the 6EP1 434-2BA00 (the item you linked us to with that google search) is supposed to use 400V to 500V 3-phase as input, not 230V single phase.

So what power supply are you actually using?
0
 

Author Comment

by:pr2501
ID: 37740995
The picturit  was just simbolic the real one  (see above (the last one: recifer) is:
6EP -1334-2BA00.  I did not expect to cause confiuson, i was yust looking for some
24 DC Siemens power suply.


Maybe more about procces: The welding machine uses to start welding  betwen two points high electric potencial diference (around 10000V). This tension diference produces spark
betwen two electrodes an then curent begin to flow.
This tension produces high magnetic field into machine cel.
0
 
LVL 44

Accepted Solution

by:
Darr247 earned 2000 total points
ID: 37742812
OK... that's a 24V 10A power supply.

Replace the existing load wire with SHIELDED cable such as Belden 3072F (18AWG will easily handle 14A at the 'blue hose' rating of 75 degrees C) and ground the shield on ONE END ONLY.

Grounding both ends of the shield essentially turns it into an antenna, which can often be worse than using unshielded wiring. Typically you ground the shield just by connecting to earth the bare 'drain' wire that runs the length of the cable in contact with the shield.


I found that particular cable online for between $1.50 and $2 per foot.
I can't put that into localized units because EE no longer shows the poster's time zone and you never told us where you were.
0
 

Author Comment

by:pr2501
ID: 37756504
We have to stop machine for more days to replace all cables. We well do it next month.

For the test i have used testing sistem by independent  recifer and two cables: one SHIELDED and another not. And i had put them together with "old" cables. I had made some measurments and the signal on the shilded cable was better. Still noise persist but much lower.

So i preume that shilded cables will resolve the problem.

Thank you.
0
 
LVL 44

Expert Comment

by:Darr247
ID: 37757036
It wouldn't hurt to put those 1uF 'snubber' filter caps on all inductive loads that turn on/off often (such as across control relay coils), too.

I would only use the ferrite bead inductors/chokes on sensitive components that are affected by those few-cycle spikes being induced by the welder flux, if there is any left once the wires are shielded.
0
 

Author Comment

by:pr2501
ID: 37757152
Ok, thank You. I will let You know  the result.
0

Featured Post

Ready for your healthcare security check-up?

In the past few years, healthcare organizations have become a prime target for advanced attacks. Does your organization have what it needs to defend itself? Schedule your healthcare security check-up today and download our free Healthcare Security Resource Kit today!

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Every server (virtual or physical) needs a console: and the console can be provided through hardware directly connected, software for remote connections, local connections, through a KVM, etc. This document explains the different types of consol…
Arrow Electronics was searching for a KVM  (Keyboard/Video/Mouse) switch that could display on one single monitor the current status of all units being tested on the rack.
Please read the paragraph below before following the instructions in the video — there are important caveats in the paragraph that I did not mention in the video. If your PaperPort 12 or PaperPort 14 is failing to start, or crashing, or hanging, …
Is your data getting by on basic protection measures? In today’s climate of debilitating malware and ransomware—like WannaCry—that may not be enough. You need to establish more than basics, like a recovery plan that protects both data and endpoints.…
Suggested Courses

916 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question