Protecting servers from water sprinklers in a server room

Posted on 2013-05-23
4
1,347 Views
Last Modified: 2013-05-27
I was informed by the building management that they will be installing sprinkers in every room. I am worried that a trash bin fire or false alarm is going to cause the servers to get wet.    How do do we protect the server racks from water from the sprinkers?

Grrrr
0
Comment
Question by:masterofall
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
  • 2
4 Comments
 
LVL 31

Assisted Solution

by:Scott C
Scott C earned 167 total points
ID: 39191837
In our server room we have a Halon system instead of water.  Water is for the rest of the building.

It would probably be expensive, but you may want to see if your building management would want to go this route.  After all, even if you were able to cover your server with plastic the trapped air might cause them to overheat.

And that is assuming whatever method you choose to protect your servers actually works.  Even a little water will cause tons of damage.

Make sure you have a good backup routine and keep your backups offsite.  If it all hits the fan at least you will have your backups to rebuild everything.
0
 
LVL 6

Accepted Solution

by:
insidetech earned 333 total points
ID: 39191867
You can ask for special exception for that space. If it is mandated that this particular room must have fire protection... your option, though very expensive would be to use something like inert gases and halocarbon compound fire suppression but this is something you will have to defer to fire protection professionals to be in accordance with local codes etc.
0
 
LVL 6

Assisted Solution

by:insidetech
insidetech earned 333 total points
ID: 39192692
Just FYI Halon as a fire suppressant has been outlawed in US and for that matter around the world since 1989! It is allowed only in grandfathered systems and frowned upon as ozone depleting substance.
0
 
LVL 1

Author Comment

by:masterofall
ID: 39192984
The building managers says that each sprinkler operates independently and each will only activate if the temperature reaches 200 degrees.  Sprinklers are going on everyfloor including the floor above  the server room. The best right now is to put everything inside the racks and close all sides of the rack except the back mesh.   I will have to find some creative way to protect the racks from flood and dripping water and also look at waterproof racks. For example http://szeton.en.alibaba.com/product/474878009-212375807/27U_waterproof_outdoor_server_racks_cabinets.html
0

Featured Post

Ransomware: The New Cyber Threat & How to Stop It

This infographic explains ransomware, type of malware that blocks access to your files or your systems and holds them hostage until a ransom is paid. It also examines the different types of ransomware and explains what you can do to thwart this sinister online threat.  

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Moving your enterprise fax infrastructure from in-house fax machines and servers to the cloud makes sense — from both an efficiency and productivity standpoint. But does migrating to a cloud fax solution mean you will no longer be able to send or re…
Great sound, comfort and fit, excellent build quality, versatility, compatibility. These are just some of the many reasons for choosing a headset from Sennheiser.
In this brief tutorial Pawel from AdRem Software explains how you can quickly find out which services are running on your network, or what are the IP addresses of servers responsible for each service. Software used is freeware NetCrunch Tools (https…
Sometimes it takes a new vantage point, apart from our everyday security practices, to truly see our Active Directory (AD) vulnerabilities. We get used to implementing the same techniques and checking the same areas for a breach. This pattern can re…

623 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question