Solved

Server Power usage - Watts to Amps

Posted on 2013-11-08
9
1,140 Views
Last Modified: 2013-11-19
I have a rack of servers which I am trying to consolidate. I have an APC meter which is not configured, but it does give us a amp reading.

Anyhow, I was looking at the Hp specs and it seems like my most powerful server (DL380 G4) uses 575 WATTS. I tried to convert this to amps using several calculators i found via search engines..but i don't trust the output of the calculators - or maybe my math is not correct.

How can I calculate how much amperage my servers are using based on Hp specs sheets?

although I have an apc meter, at the moment I cannot configure this in order to read exact readings due to the fact that I am far away from my data center.


      
Specification
Power Supply
      
575 Watt, CE Mark Compliant
Rated Input Voltage
      
100-132 VAC, 200-240 VAC
Rated Input Current
      
7.5A (100VAC), 3.8A (200VAC)
Rated Input Frequency
      
50 to 60 Hz
Rated Input Power
      
735 W
Rated Steady-State Power
      
575W
Maximum Peak Power
      
575W
Operational Input Voltage Range (Vrms)
      
90 - 264
Frequency Range (Nominal) (Hz)
      
47 - 63 (50/60)
--
thx
t
0
Comment
Question by:tobe1424
9 Comments
 
LVL 88

Expert Comment

by:rindi
ID: 39634068
Ampere times Volts will give you the Watts. Normally though Watts are only used for DC type current. For AC type current you use VA (Volt Ampere), but also here it's the same equation.
0
 

Author Comment

by:tobe1424
ID: 39634108
Based on the specs in my first post, would i be able to figure out the ampere?

thx
0
 
LVL 32

Accepted Solution

by:
_ earned 250 total points
ID: 39634167
Not really.
You can get the Maximum by dividing the Watts by the Voltage (which looks like the AC amps is already posted).

The only way to really get the Actual draw, is with a meter.


Specification

Power Supply
575 Watt, CE Mark Compliant

Rated Input Voltage
100-132 VAC, 200-240 VAC

Rated Input Current
7.5A (100VAC), 3.8A (200VAC)


Rated Input Frequency
50 to 60 Hz

Rated Input Power
735 W

Rated Steady-State Power
575W

Maximum Peak Power
575W

Operational Input Voltage Range (Vrms)
90 - 264

Frequency Range (Nominal) (Hz)
47 - 63 (50/60)
0
Netscaler Common Configuration How To guides

If you use NetScaler you will want to see these guides. The NetScaler How To Guides show administrators how to get NetScaler up and configured by providing instructions for common scenarios and some not so common ones.

 

Author Comment

by:tobe1424
ID: 39634208
ahhh...so the  7.5A rating is theoretically the MAX ampere the server could possibly draw?

I see how the meter would help with specifics. My APC meter states we are consuming about 23 amps. I have about 10 servers + network equipment on my 42U rack.

I assume when the servers power up, more amp is drawn..

thx
0
 
LVL 83

Assisted Solution

by:Dave Baldwin
Dave Baldwin earned 250 total points
ID: 39634209
According to the specs you have posted, that computer uses 735W to produce 575W internally.  Your electrical load is the 735W.  The difference is because power supplies are not 100% efficient.  The Rated Input Current that coral highlighted is what you need to be able to provide.
0
 
LVL 55

Expert Comment

by:andyalder
ID: 39634662
You cannot use the PSUs ratings to determine the power that the server will use since it's rated far higher than is needed in most configurations. What you have to do instead is use HP's (or APCs) power calculator. HP's calculators seem to have been highjacked by the G8 marketing team but APCs UPS selector ought to work still.
0
 

Author Comment

by:tobe1424
ID: 39634810
thanks much for the help.

I have all my servers on apc pdu's (ap7801) . they have a visual amp reading. i guess i can remote into these and see the power rating on each exact port?
0
 
LVL 32

Expert Comment

by:_
ID: 39634946
I'm not familiar with the 7801's, but I'm going with a tentative yes.

Just remember, you are dealing with 2 sets of current.
The AC coming in from the wall (through the UPS and into the computers power supply). This will usually have "high" volts and "low" amps.

Then there's the DC the computers uses internally, coming out of the power supply. This is usually "low" volts, and "high" amps.

Be careful not to get the numbers mixed up.   ; )


>> I assume when the servers power up, more amp is drawn...

Correct, but usually for less than a minute. Once all the HDDs, ram, video, etc, get 'up to speed', it should drop back down.
0
 
LVL 32

Expert Comment

by:_
ID: 39661317
Thank you much.     : )
0

Featured Post

PRTG Network Monitor: Intuitive Network Monitoring

Network Monitoring is essential to ensure that computer systems and network devices are running. Use PRTG to monitor LANs, servers, websites, applications and devices, bandwidth, virtual environments, remote systems, IoT, and many more. PRTG is easy to set up & use.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Every server (virtual or physical) needs a console: and the console can be provided through hardware directly connected, software for remote connections, local connections, through a KVM, etc. This document explains the different types of consol…
A procedure for exporting installed hotfix details of remote computers using powershell
This tutorial will give a short introduction and overview of Backup Exec 2012 and how to navigate and perform basic functions. Click on the Backup Exec button in the upper left corner. From here, are global settings for the application such as conne…
To efficiently enable the rotation of USB drives for backups, storage pools need to be created. This way no matter which USB drive is installed, the backups will successfully write without any administrative intervention. Multiple USB devices need t…

770 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question