redundant power supply

Posted on 2013-11-22
9
601 Views
Last Modified: 2013-11-29
Is there any easy way to check if a physical server has a redundant power supply that is working? How can you request evidence of this. Can anyone give an idiots guide of how and when you need a redundant power supply - how common is it for the main power supply to fail? Whats the risk in not having a redundant power supply?
0
Comment
Question by:pma111
  • 5
  • 3
9 Comments
 
LVL 25

Assisted Solution

by:Mohammed Khawaja
Mohammed Khawaja earned 250 total points
ID: 39668664
Yes there is easy way of checking.  What you need to do is inventory your sever, check the specs by contacting the vendor and also note that vendors do provide management software which could tell you if there are redundant software or not.  If according to your investigation, power supplies are redundant then testing would require either removing the power supply or the power cord while the server is on.
0
 
LVL 32

Accepted Solution

by:
PowerEdgeTech earned 250 total points
ID: 39668941
There are several ways - physically and through software - to check if your server has redundant power supplies, but it would be helpful to know the make/model of the servers.

Does your server have two plugs?  If so, it most likely has redundant power supplies.  If one is not working, most systems will give you an error message related to it.

Why would you need redundant power supplies?  It is not super common for power supplies to fail, but it is probably the next most common part to hard drives to fail ... if you lose power, game is over until it is replaced.  Having redundant power supplies is an EASY way to mitigate the possibility of a power supply failure or loss of "house" power (where the other one would be connected to a UPS).
0
 
LVL 3

Author Comment

by:pma111
ID: 39668958
Hi, its a hewlett packard ProLiant DL360 G5
0
NAS Cloud Backup Strategies

This article explains backup scenarios when using network storage. We review the so-called “3-2-1 strategy” and summarize the methods you can use to send NAS data to the cloud

 
LVL 3

Author Comment

by:pma111
ID: 39668965
I dont have access to the server room its for a risk assessment process.
0
 
LVL 3

Author Comment

by:pma111
ID: 39668991
Completely new to this but can you have a redundant power supply feature in your server but not use it? i.e. just because the server supports 2 power supplies does that mean the IT team are actually using them?
0
 
LVL 3

Author Comment

by:pma111
ID: 39669000
And what is failing, is it something in the server, or we on about the actual AC socket the cable is plugged into (from the server).
0
 
LVL 32

Expert Comment

by:PowerEdgeTech
ID: 39669024
Yes, you can have redundant power supplies and not use them, but unless they are able to unseat or disable one, they will get an error message if it is there and not connected to power.

"And what is failing, is it something in the server, or we on about the actual AC socket the cable is plugged into (from the server). "

Both.  Failure could be failure of the power supply unit itself, the cable, the outlet/UPS, power from the city, etc.
0
 
LVL 3

Author Comment

by:pma111
ID: 39669040
Would you help assist as to whether HP ProLiant DL360 G5 has redundant power supply facilities? And perhaps how to check they are enabled/in use on the server?
0
 
LVL 32

Expert Comment

by:PowerEdgeTech
ID: 39669383
I'm not familiar with HP servers, but according to the specs, it has the capability:
http://h18004.www1.hp.com/products/quickspecs/12476_na/12476_na.pdf

Do you have remote access to the server?  If so, AND you have HP's management software installed (I don't know what this is called), you can view the power supplies installed and their status.

You can also probably get the serial number and look up the original order details to see if it shipped with the redundant power supply option.
0

Featured Post

Netscaler Common Configuration How To guides

If you use NetScaler you will want to see these guides. The NetScaler How To Guides show administrators how to get NetScaler up and configured by providing instructions for common scenarios and some not so common ones.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Suggested Solutions

In this article we have discussed the manual scenarios to recover data from Windows 10 through some backup and recovery tools which are offered by it.
In the modern office, employees tend to move around the workplace a lot more freely. Conferences, collaborative groups, flexible seating and working from home require a new level of mobility. Technology has not only changed the behavior and the expe…
In an interesting question (https://www.experts-exchange.com/questions/29008360/) here at Experts Exchange, a member asked how to split a single image into multiple images. The primary usage for this is to place many photographs on a flatbed scanner…

856 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question