Experts,

I was thinking to place two desktop computers on a 600VA UPS with 15 mins backup time. The reason for this is to save on cost as I only need to 10 seconds backup time before the generator would kick in. Is there any concern with this setup?

I calculated the watts and each CPU needs 280watts, LCD needs 300watts. Current voltage is 220v.
0
Comment
Question by:gsmith888
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
9 Comments
 
LVL 40

Accepted Solution

by:
als315 earned 800 total points
ID: 39751550
Real power of 600VA UPS will be 600*0.8=480 watts
0
 

Author Comment

by:gsmith888
ID: 39751557
If I exceeded the real power of 480watts and backup time is 15 mins on full load, I'm assuming the back up time will reduce in half? Or I have this all wrong and the UPS will not work?
0
 
LVL 97

Assisted Solution

by:Experienced Member
Experienced Member earned 400 total points
ID: 39751604
Are you sure your LCD needs 300 watts? That seems high.

Nonetheless a 600VA UPS would be good for one computer and LCD display.

I have an APC Smart UPS 750 and it services a computer, LCD display and network. I easily get 15 minutes out of, probably a bit more.

If all you wish to do is shut computers down in less than 1 minute, then the 600VA will service 2 computers and displays quite well.  This is based on the computers not using their rated capacity.

If you overload a UPS (total current) it will shut down to avoid damage.

... Thinkpads_User
0
WatchGuard's M Series Appliances - Miecom Approved

WatchGuard's newest M series appliances were put to the test by Miercom.  We had great results and outperformed all of our competitors in both stateless and stateful traffic throghput scenarios! Ready to see how your UTM appliance stacked up? Download the Miercom Report!

 
LVL 34

Expert Comment

by:Paul MacDonald
ID: 39751614
The actual run time will depend on how much power - in watts - you're drawing, and we have no way of knowing that.  However, I'd wager you could run two computers off the UPS for 15 seconds.  You can test this by plugging in all the equipment to the UPS, then unplugging the UPS from the wall and timing how long the equipment runs on battery only.
0
 
LVL 56

Assisted Solution

by:andyalder
andyalder earned 400 total points
ID: 39751665
You cannot exceed the VA rating of the UPS or it will just trip out. 600VA doesn't sound enough for two desktop PCs although some new PCs don't take much more current than laptops.
0
 
LVL 6

Expert Comment

by:insidetech
ID: 39751767
Exclude the monitors from using the UPS battery. Plug them in to the surge protection portion of the UPS.
For what it is worth the PF of switching power supplies is much higher than .8 but that is academic  in this scenario.
Plug both computers in, unplug and test. If it works GREAT! If not... Get two ;-)
0
 
LVL 44

Assisted Solution

by:Darr247
Darr247 earned 400 total points
ID: 39751774
600VA sounds like the $50 units BestBuy sells to keep your TV and DVR going while the generator kicks in. Use one for each computer, or else go to one a little heavier.
e.g. CyberPower 1500VA UPS. I realize 220V is not the most-common voltage seen in the USA, but if you want localized answers, you need to tell us where you're located. :)
0
 
LVL 92

Expert Comment

by:nobus
ID: 39753246
and also check if you don't exceed the output current of the UPS
the startup current could be a problem; but only 1 way to know = test
0
 
LVL 40

Assisted Solution

by:als315
als315 earned 800 total points
ID: 39753300
You can try UPS selector from APC (you can select your country):
http://www.apc.com/tools/ups_selector/NO/no/home/load
There are 2 parameters of UPS: load (watts or VA) and battery capacity (time on battery).
You can't exceed load (good UPS will be switched off immediately if load exceeds real power of UPS, when cheep UPS may work, but voltage may be wrong).
0

Featured Post

Industry Leaders: We Want Your Opinion!

We value your feedback.

Take our survey and automatically be enter to win anyone of the following:
Yeti Cooler, Amazon eGift Card, and Movie eGift Card!

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Data center, now-a-days, is referred as the home of all the advanced technologies. In-fact, most of the businesses are now establishing their entire organizational structure around the IT capabilities.
Or at least that’s the word according to a new blog from Tech Target on AWS’s new Managed Services (MS) offering. According to the blog, AWS is launching their AWS MS program to expedite the adoption of cloud by Fortune 1000 and Global 2000 companie…
In this video, Percona Director of Solution Engineering Jon Tobin discusses the function and features of Percona Server for MongoDB. How Percona can help Percona can help you determine if Percona Server for MongoDB is the right solution for …
In this video, Percona Solutions Engineer Barrett Chambers discusses some of the basic syntax differences between MySQL and MongoDB. To learn more check out our webinar on MongoDB administration for MySQL DBA: https://www.percona.com/resources/we…

801 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question