Solved

EMC - Storage Array Error

Posted on 2014-02-12
4
841 Views
Last Modified: 2014-02-21
Hi there,

We have a CX3-80 and we started getting this error last week and we continuously get it a few times every day.  Any suggestions?

Time Stamp 02/12/14 14:52:36 (GMT) Event Number 71174001 Severity Warning Host CX3-PROC-A Storage Array APM00070904191 SP N/A Device N/A Description SFP Diagnostic condition "Transmit bias high warning" detected for physical port 2
 00 00 04 00 03 00 56 00 d3 04 00 00 01 40 17 a1 01 40 17 a1 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 71 17 40 01

Thanks,
- Christian
0
Comment
Question by:Christian Palacios
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
  • 3
4 Comments
 
LVL 30

Assisted Solution

by:Duncan Meyers
Duncan Meyers earned 500 total points
ID: 39854348
That suggests that the SFP on  Port 2 on SPB is failing. You *may* also see CRC errors or similar on the matching port on the connected fibre channel switch.

I'd call it in to EMC and get the storage processor replaced. The SFP are fixed on a CX3-80, so the whole unit had to be replaced.
0
 

Author Comment

by:Christian Palacios
ID: 39868828
Hi Duncan,

Thank you.  What is the SFP?  If it fails, what can/could occur?  When you mean unit, do you mean the entire CX3-80 unit, not a hot-swappable part of the CX3-80 unit??

Thanks,
- Christian
0
 
LVL 30

Accepted Solution

by:
Duncan Meyers earned 500 total points
ID: 39868975
SFP = Small Form-factor Pluggable - the optical transceiver module that the FC cable plugs into. Often incorrectly referred to as a GBIC (Giga Bit Interface Converter) - on a CX3-80, it's soldered onto the storage processor board.

In this case, the unit is the affected storage processor sub assembly. It's 100% hot-swappable, but I'd recommend doing the swap at a quiet time as the replacement will temporarily affect array performance - and it obviously temporarily reduces redundancy. You should perform a couple of pre-checks before swapping a storage processor board. Check that the path balancing algorithm in VMware is set correctly (should be Round Robin or MRU) and for physical hosts, check that PowerPath is happy and reporting that paths are alive. If all that checks out OK, then the hosts will cope with losing a storage processor and LUNs will fail over correctly. You could also do a pre-emptive trespass of all LUNs on the faulty storage processor to its partner. To force a trespass (this is non-disruptive), right-click on the LUN in Unisphere or Navisphere and select Trespass.
0
 
LVL 30

Expert Comment

by:Duncan Meyers
ID: 39868999
Sorry - missed this bit: if the SFP fails, the array will continue to operate normally and whatever path balancing/path fail-over software you have will route FC frames down other paths to the arrays, but you've lost a level of redundancy and if you're working the array hard, you've potentially lost some performance too.
0

Featured Post

Simplifying Server Workload Migrations

This use case outlines the migration challenges that organizations face and how the Acronis AnyData Engine supports physical-to-physical (P2P), physical-to-virtual (P2V), virtual to physical (V2P), and cross-virtual (V2V) migration scenarios to address these challenges.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Suggested Solutions

I previously wrote an article addressing the use of UBCD4WIN and SARDU. All are great, but I have always been an advocate of SARDU. Recently it was suggested that I go back and take a look at Easy2Boot in comparison.
Many businesses neglect disaster recovery and treat it as an after-thought. I can tell you first hand that data will be lost, hard drives die, servers will be hacked, and careless (or malicious) employees can ruin your data.
This video teaches viewers how to encrypt an external drive that requires a password to read and edit the drive. All tasks are done in Disk Utility. Plug in the external drive you wish to encrypt: Make sure all previous data on the drive has been …
This tutorial will walk an individual through the process of installing the necessary services and then configuring a Windows Server 2012 system as an iSCSI target. To install the necessary roles, go to Server Manager, and select Add Roles and Featu…

749 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question