I have been tasked with finding out how many amps all of our server room equipment pulls.  How to tackle this?

Posted on 2014-04-09
3
449 Views
Last Modified: 2015-11-03
I'm not an electrician, not even close, and I'm unsure of the fastest and most efficient way to accomplish, but unfortunately I need to have answers by today.  We have about 30 pieces of equipment between routers, servers, and switches in our data room.  Any advice would be GREATLY appreciated.
0
Comment
Question by:LB1234
3 Comments
 
LVL 34

Accepted Solution

by:
Paul MacDonald earned 500 total points
ID: 39989124
All your equipment should list its amperage on a tag somewhere on the equipment.  Add that all up and Bob's your uncle.  This number should be a maximum and will likely exceed your actual usage.

If that's not practical/possible, a device like this (and there are many) will give you an idea of what a device is actually drawing at the time you measure.
0
 
LVL 30

Expert Comment

by:Duncan Meyers
ID: 39993298
Manufacturer's stated maximum current is exactly that: a maximum for a fully configured system with every conceivable option loaded in at the highest load. if you calculate the current consumption based on that, you'll be out by at least 50% and probably significantly more. A much more accurate method is to use an ammeter to measure the actual consumption. You should measure the power consumed by all racks and air conditioning as well

A clamp meter only works if you can separate the active and neutral conductors which you can do at the switch board - but for heaven's sake, call a licensed electrician to do this for you. Don't access the wiring behind the covers on the switchboard unless you know **exactly** what you're doing. If you get it wrong at best you'll cause a massive outage. At worst, you'll be pushing up daisies.
0
 
LVL 7

Expert Comment

by:Casey Weaver
ID: 41181107
If your servers have something like DELL Openmanage or HP ILO, that system will give you current, if not historical as well, power data. As for other pieces of equipment, like switches and routers, they won't. If you need numbers, you won't really be able to get them today. You would need an electrician to come out with a meter and he would have to tap into your breakers that run your server room. If this is something you'll continue to need, you'll need to buy smart PDU's and get them wired onto all of the equipment, and into your network. You can buy per outlet models, that give power draw by outlet: https://www.apc.com/products/family/index.cfm?id=478  Or you can get much cheaper and buy a unit that just tells you power draw for the entire PDU: https://www.apc.com/products/family/index.cfm?id=136
0

Featured Post

U.S. Department of Agriculture and Acronis Access

With the new era of mobile computing, smartphones and tablets, wireless communications and cloud services, the USDA sought to take advantage of a mobilized workforce and the blurring lines between personal and corporate computing resources.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Monitor input from a computer is usually nothing special.  In this instance it prevented anyone from using the computer.  This was a preconfiguration that didn't work.
Data center, now-a-days, is referred as the home of all the advanced technologies. In-fact, most of the businesses are now establishing their entire organizational structure around the IT capabilities.
Finds all prime numbers in a range requested and places them in a public primes() array. I've demostrated a template size of 30 (2 * 3 * 5) but larger templates can be built such 210  (2 * 3 * 5 * 7) or 2310  (2 * 3 * 5 * 7 * 11). The larger templa‚Ķ

777 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question