I have the following error with the UPS which gives power to switches:

According to documentation (http://www.fusionps.com.au/ProductDocuments/106/Eaton_EX_2200-3000_Product_Manual.pdf), when this error occurs:

LED (22) is ON,
the alphanumeric display indicates:
INTERNAL FAULT
SERV REQUIRED


The reason is:

A UPS internal fault has occurred.
There are two possible situations:

the load is still supplied, but
directly with AC input power via
the bypass,

the load is no longer supplied.


Recommendation

Call the after-sales support
department.


Switches and internet are working properly.
0
Comment
Question by:Nusrat Nuriyev
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
  • 2
3 Comments
 
LVL 97

Assisted Solution

by:Experienced Member
Experienced Member earned 1000 total points
ID: 40323011
What is the question?   The unit needs service. The batteries could have failed or the circuitry could have developed a fault.
0
 
LVL 19

Accepted Solution

by:
Miguel Angel Perez Muñoz earned 1000 total points
ID: 40323123
Usually  UPS found an internal problem (inverter failure or similar) and autobypassed by itself to continue powering your "protected" load.
On this condition, some electrical interference will be delivered to protected equipment, UPS can filter anything because is bypassed.
As said John, call support.
0
 
LVL 97

Expert Comment

by:Experienced Member
ID: 40335194
@Nusrat Nuriyev  - Good luck with getting the unit serviced. I was happy to help you with this.
0

Featured Post

Turn your laptop into a mobile console!

The CV211 Laptop USB Console Adapter provides a direct Laptop-to-Computer connection for fast and easy remote desktop access with no software to install.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

INTRODUCTION The purpose of this document is to demonstrate the Installation and configuration, of the HP EVA 4400 SAN Storage. The name , IP and the WWN ID’s used here are not the real ones. ABOUT THE STORAGE For most of you reading this, you …
Usually shares are where we want them for our users and we tend to take them for granted. There are times, however, when those shares may disappear causing difficulty for your users. One of the first things to try is searching for files that shou…
In this video, Percona Director of Solution Engineering Jon Tobin discusses the function and features of Percona Server for MongoDB. How Percona can help Percona can help you determine if Percona Server for MongoDB is the right solution for …
In this video, Percona Solutions Engineer Barrett Chambers discusses some of the basic syntax differences between MySQL and MongoDB. To learn more check out our webinar on MongoDB administration for MySQL DBA: https://www.percona.com/resources/we…
Suggested Courses

765 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question