Dear experts,

Recently the company wishes to relocate the servers. I may need some suggestions as in some recommendations with the server room space.

1. server room has a small ventilation (1x1ft) for cool air to come into the server room when AC is turned on.
2. server room does not have a door and the room dimension is 10x15 ft.
3.  there will be a portable server rack 42in along with a wall mount of 12in for panels routes, firewall, and switches. All these are aligned to a single side of the wall. IP phone system is just adjacent to the server and mounted on the same wall.
4. overall the server room is very spacious (big enough to circumvent) .

My question is that with a open sector (server room has no door), will it be better to utilize fans (as in any types of fans such as ones can be mounted on the server or just buy  bigger fans to circumvent the room?

What are some Pros and Cons of using this method?

Due to the structure of the building, there is no way to alter the air ducts in any way and what will be other alternative options available?

Thanks
0
Comment
Question by:Kinderly Wade
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
2 Comments
 
LVL 13

Accepted Solution

by:
akb earned 500 total points
ID: 40414470
I would just install the rack and see how it goes. If the room is comfortable enough for people to occupy it is probably OK for the equipment in your rack.
Fans are unlikely to cool the room - they will only move the air around. This may cause dust to get sucked into the rack by the fans in the equipment inside the rack.
If the servers generate a little too much heat for the rack you could put some fans in the top of the rack to help remove the heat. Many racks are designed to allow fans to be installed at the top.
If heat is a real problem you may be able to build a partition wall and door to divide the rack area from the rest of the room and install a heat pump (air conditioner) to keep that area cool.
0
 
LVL 32

Expert Comment

by:aleghart
ID: 40420822
A general way to figure out if a small room will get too hot:

A sitting office worker generates ~300 BTU/hr (~100 W).   Figure out how many BTU your equipment will be generating.  Divide by 300.

So, if your equipment will draw 1,000W, that will be ~3,400 BTU/hr.  That's around 10 people.

Can that room comfortably hold 10 people, without all of the equipment?

2,000W would be 20 people.  3,000W...30 people.

A 12in X 12in register does not sound like much cool air entering the room.

Figure, if this was a party at your house...my living room can hold 5-6 people and stay cool.  10 people...getting a little warm.  20 people...the air conditioning cannot keep up.
0

Featured Post

Save the day with this special offer from ATEN!

Save 30% on the CV211 using promo code EXPERTS30 now through April 30th. The ATEN CV211 connects a laptop directly to any server allowing you instant access to perform data maintenance and local operations, for quick troubleshooting, updating, service and repair.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Suggested Solutions

Title # Comments Views Activity
physical server is showing red light on few drives 20 109
IPV6 Issues 3 48
2008 SBS renaming user accounts? 3 61
In a Raid can I operate with failing hard drives 17 102
INTRODUCTION The purpose of this document is to demonstrate the Installation and configuration, of the HP EVA 4400 SAN Storage. The name , IP and the WWN ID’s used here are not the real ones. ABOUT THE STORAGE For most of you reading this, you …
Because virtualization becomes more and more common, and, with Microsoft Hyper-V included in Windows Server at no additional costs, and, most server hardware nowadays is more than capable of running a physical Small Business Server (SBS) 2008 or 201…
The Email Laundry PDF encryption service allows companies to send confidential encrypted  emails to anybody. The PDF document can also contain attachments that are embedded in the encrypted PDF. The password is randomly generated by The Email Laundr…

732 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question