We are setting up Juniper SRX240H2.  The user guide says that before turning power, the gateway needs to be grounded first. Anyone have any experience with this?  The SRX210 model only suggests grounding the device, but the manual for the Juniper SRX240 seems pretty adamant about grounding the device before turning on the power.  Here is an excerpt from the manual.

The following tools and parts are required for grounding the SRX240 Services Gateway:
∙Grounding cable for your services gateway—The grounding cable must be minimum 14 AWG (2 mm²), minimum 90°C wire, or as permitted by the local code.
∙Grounding lug—Ring-type, vinyl-insulated TV14-6R lug or equivalent for your grounding cable
∙Washers and 10-32x.25-in. screws to secure the grounding lug to the protective earthing terminal
0
Comment
Question by:joharazad
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
3 Comments
 
LVL 26

Assisted Solution

by:Fred Marshall
Fred Marshall earned 668 total points
ID: 40468402
Nobody is going to tell you NOT TO do this.
I have experience in that I didn't read those instructions and I can't report any bad results with our SRX240H2.

So, the answer to your direct question is : Yes, we have experience.

Is there more?
0
 
LVL 32

Assisted Solution

by:dpk_wal
dpk_wal earned 668 total points
ID: 40468823
As already commented; we have used multiple SRX240 without ever grounding them. The srx240 are working fine without reporting issues.

It is always a good practice to ground the electrical equipment so that ESD does not harm the equipment.

Thank you.
0
 
LVL 32

Accepted Solution

by:
harbor235 earned 664 total points
ID: 40473881
If you are racking this device and the rack is properly  grounded properly there is no need to ground this device individually.
However, my assumption is that each individual rack is grounded per industry standards?

http://www.cablinginstall.com/articles/print/volume-15/issue-12/features/installation/grounding-and-bonding-questions-answered.html


harbor235 ;-}
0

Featured Post

Free Tool: Port Scanner

Check which ports are open to the outside world. Helps make sure that your firewall rules are working as intended.

One of a set of tools we are providing to everyone as a way of saying thank you for being a part of the community.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Before I go to far, let's explain HA (High Availability) and why you should consider it.  High availability is the mechanism used to provide redundancy to any service at the same site and appears as a single service to the users of that service.  As…
#Citrix #Netscaler #MSSQL #Load Balance
In this video we outline the Physical Segments view of NetCrunch network monitor. By following this brief how-to video, you will be able to learn how NetCrunch visualizes your network, how granular is the information collected, as well as where to f…
In this video you will find out how to export Office 365 mailboxes using the built in eDiscovery tool. Bear in mind that although this method might be useful in some cases, using PST files as Office 365 backup is troublesome in a long run (more on t…
Suggested Courses
Course of the Month10 days, 14 hours left to enroll

770 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question