Dear Experts,

I attached two designs of two Data centers, both have raised floor, I need to specify the best location to fix the tem.,humidity,water leakage and smoke detector sensors plus the camera pods.

Thanks in Advance,
P.jpg
B.jpg
0
Comment
Question by:oamal2001
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
9 Comments
 
LVL 62

Expert Comment

by:gheist
ID: 40520028
Normally you have UPS per rack. That adds value as electricity splitter.
Will the unit blamed AC in your drawing be pulling air on top and blowing on the ground to help abuse natural circilation?
Normally servers blow hot air in the back FYI. I dont see that instrumented at all.
0
 

Author Comment

by:oamal2001
ID: 40520255
The UPS is centrally installed together with a generator, the air flow will be from down, the front of the racks will be faced to the AC unit.

Thanks,
0
 
LVL 62

Expert Comment

by:gheist
ID: 40520271
wrong air flow costs you 1kW per rack 24x7
0
Optimize your web performance

What's in the eBook?
- Full list of reasons for poor performance
- Ultimate measures to speed things up
- Primary web monitoring types
- KPIs you should be monitoring in order to increase your ROI

 

Author Comment

by:oamal2001
ID: 40520275
what about the sensors I mentioned, where are the best locations?

Thanks,
0
 

Author Comment

by:oamal2001
ID: 40520317
Do you have a better design that could be done with the same UPS and AC?

Thanks,
0
 
LVL 62

Expert Comment

by:gheist
ID: 40520428
Each server has sensor or fifty, You will have tons of time to record them.

What I can suggest that you arrange air flows right. i.e cold air is blown in the face of servers from bellow and droppings are collected behind on top and front and back is isolated with slaughterhouse curitains.
https://www.google.com/about/datacenters/efficiency/external/?hl=en
0
 
LVL 30

Expert Comment

by:Kerem ERSOY
ID: 40521000
Hi,

First of all it is preferable to have FM200 units out of the rooms. This is because if a fire occurs it might destroy the sensors or lines or worst cause the the tanks to explode. You also need to have control units and operating panels outside the room and make sure that doors are equipped with emergency panic bars. This is because FM200 gas removes the oxygen from the environment to extinguish any fire rapidly which is dangerous for humans. Should FM200 is activated it is preferable for people to control/override the operation from outside.

Then we come to other sensors.

General rule of thumb for cameras:
You generally use cameras to determine  who has accessed some rack/server and/or who entered the room. So that you could detect any unauthorized access to them. Cams should be placed on points where:
- You can record any person who enters/exits the room.
- Back/front of each rack so that you would know who had accessed to a particular/rack server at a specific time.

Humidity Sensors:
- If there's a water leakage it would most probably comes from the floor because you use FM-200 gas to extinguish any fire and your nozzles would not have any liquid. So the best place would be under the raised floor over the surface of the room.  They should be placed especially under the AC assuming that you're using precision A/C which utilizes water, and Racks in case there's a problem with water.

Smoke detectors would be placed over the ceiling close to Racks and the A/C.


Cheers,
K.
0
 
LVL 62

Expert Comment

by:gheist
ID: 40521141
But you dont want to film passwords or screens.
0
 
LVL 25

Accepted Solution

by:
madunix earned 2000 total points
ID: 40526696
Data Centerhttps://www.serverscheck.com/seo/dcim.asp

Under floor of data centre you may have electrical and power cable...that is the reason you should place water detectors under raised floor also....humidity control is required for servers which are placed above raised floor; as stated in the above link "Maintaining equipment at the optimum climate range aids in protecting hardware from corrosion problems associated with high humidity levels and failures caused by static discharge when humidity is too low."
0

Featured Post

WordPress Tutorial 1: Installation & Setup

WordPress is a very popular option for running your web site and can be used to get your content online quickly for the world to see. This guide will walk you through installing the WordPress server software and the initial setup process.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

This article explains the fundamentals of industrial networking which ultimately is the backbone network which is providing communications for process devices like robots and other not so interesting stuff.
Introducing Priority Question, our latest feature.
There's a multitude of different network monitoring solutions out there, and you're probably wondering what makes NetCrunch so special. It's completely agentless, but does let you create an agent, if you desire. It offers powerful scalability …
Michael from AdRem Software outlines event notifications and Automatic Corrective Actions in network monitoring. Automatic Corrective Actions are scripts, which can automatically run upon discovery of a certain undesirable condition in your network.…
Suggested Courses
Course of the Month14 days, 16 hours left to enroll

771 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question