Data Center Desigh

Posted on 2014-12-27
9
269 Views
Last Modified: 2015-01-02
Dear Experts,

I attached two designs of two Data centers, both have raised floor, I need to specify the best location to fix the tem.,humidity,water leakage and smoke detector sensors plus the camera pods.

Thanks in Advance,
P.jpg
B.jpg
0
Comment
Question by:oamal2001
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
9 Comments
 
LVL 62

Expert Comment

by:gheist
ID: 40520028
Normally you have UPS per rack. That adds value as electricity splitter.
Will the unit blamed AC in your drawing be pulling air on top and blowing on the ground to help abuse natural circilation?
Normally servers blow hot air in the back FYI. I dont see that instrumented at all.
0
 

Author Comment

by:oamal2001
ID: 40520255
The UPS is centrally installed together with a generator, the air flow will be from down, the front of the racks will be faced to the AC unit.

Thanks,
0
 
LVL 62

Expert Comment

by:gheist
ID: 40520271
wrong air flow costs you 1kW per rack 24x7
0
Technology Partners: We Want Your Opinion!

We value your feedback.

Take our survey and automatically be enter to win anyone of the following:
Yeti Cooler, Amazon eGift Card, and Movie eGift Card!

 

Author Comment

by:oamal2001
ID: 40520275
what about the sensors I mentioned, where are the best locations?

Thanks,
0
 

Author Comment

by:oamal2001
ID: 40520317
Do you have a better design that could be done with the same UPS and AC?

Thanks,
0
 
LVL 62

Expert Comment

by:gheist
ID: 40520428
Each server has sensor or fifty, You will have tons of time to record them.

What I can suggest that you arrange air flows right. i.e cold air is blown in the face of servers from bellow and droppings are collected behind on top and front and back is isolated with slaughterhouse curitains.
https://www.google.com/about/datacenters/efficiency/external/?hl=en
0
 
LVL 30

Expert Comment

by:Kerem ERSOY
ID: 40521000
Hi,

First of all it is preferable to have FM200 units out of the rooms. This is because if a fire occurs it might destroy the sensors or lines or worst cause the the tanks to explode. You also need to have control units and operating panels outside the room and make sure that doors are equipped with emergency panic bars. This is because FM200 gas removes the oxygen from the environment to extinguish any fire rapidly which is dangerous for humans. Should FM200 is activated it is preferable for people to control/override the operation from outside.

Then we come to other sensors.

General rule of thumb for cameras:
You generally use cameras to determine  who has accessed some rack/server and/or who entered the room. So that you could detect any unauthorized access to them. Cams should be placed on points where:
- You can record any person who enters/exits the room.
- Back/front of each rack so that you would know who had accessed to a particular/rack server at a specific time.

Humidity Sensors:
- If there's a water leakage it would most probably comes from the floor because you use FM-200 gas to extinguish any fire and your nozzles would not have any liquid. So the best place would be under the raised floor over the surface of the room.  They should be placed especially under the AC assuming that you're using precision A/C which utilizes water, and Racks in case there's a problem with water.

Smoke detectors would be placed over the ceiling close to Racks and the A/C.


Cheers,
K.
0
 
LVL 62

Expert Comment

by:gheist
ID: 40521141
But you dont want to film passwords or screens.
0
 
LVL 25

Accepted Solution

by:
madunix earned 500 total points
ID: 40526696
Data Centerhttps://www.serverscheck.com/seo/dcim.asp

Under floor of data centre you may have electrical and power cable...that is the reason you should place water detectors under raised floor also....humidity control is required for servers which are placed above raised floor; as stated in the above link "Maintaining equipment at the optimum climate range aids in protecting hardware from corrosion problems associated with high humidity levels and failures caused by static discharge when humidity is too low."
0

Featured Post

Turn your laptop into a mobile console!

The CV211 Laptop USB Console Adapter provides a direct Laptop-to-Computer connection for fast and easy remote desktop access with no software to install.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

WARNING:   If you follow the instructions here, you will wipe out your VTP and VLAN configurations.  Make sure you have backed up your switch!!! I recently had some issues with a few low-end Cisco routers (RV325) and I opened a case with Cisco TA…
Let’s face it: one of the reasons your organization chose a SaaS solution (whether Microsoft Dynamics 365, Netsuite or SAP) is that it is subscription-based. The upkeep is done. Or so you think.
After creating this article (http://www.experts-exchange.com/articles/23699/Setup-Mikrotik-routers-with-OSPF.html), I decided to make a video (no audio) to show you how to configure the routers and run some trace routes and pings between the 7 sites…
In this video we outline the Physical Segments view of NetCrunch network monitor. By following this brief how-to video, you will be able to learn how NetCrunch visualizes your network, how granular is the information collected, as well as where to f…

695 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question