Solved

High Temperature Danger Zone for Computer Room

Posted on 2015-01-26
3
85 Views
Last Modified: 2015-06-08
We monitor our backup data center with an APC Netbotz 200 temperature/humidity unit.  Our high temperature alert is set at 84F.  Last night we received alerts that the temperature rose to 109F over 2 hours then dropped back to 82F after 4 hours.  The data center is 1000 miles away.  We were told by the hosting company that the temperature was being reported incorrectly.

1.  What is the danger zone for high temperature for a data center?
2.  Would an APC Netbotz give incorrect readings like this?  See attached graph.

Thank you,
Stuart
Screen-Shot-2015-01-26-at-6.36.12-AM.png
0
Comment
Question by:sfjcpu
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
  • 2
3 Comments
 
LVL 95

Assisted Solution

by:John Hurst
John Hurst earned 100 total points
ID: 40570406
Would an APC Netbotz give incorrect readings like this?  <-- I suggest asking APC Support about this.

More likely there was a reason (air conditioning off for a couple of hours). The hosting company should tell you what happened. I don't think their explanation is adequate.

Ask APC as the starting point, as they may give you good information to request of the hosting company.
0
 
LVL 24

Accepted Solution

by:
SunBow earned 400 total points
ID: 40570558
I suspect there's more than a tad of telling the white lie, on both sides, so you must leave room for interpretation, based on all you know.

Would you know, for example, were there power outage or potential for one (storms, APC, backup generator...), system failure (misc. outage).

My guess is that the A/C went down at begin of spike, was restored at top, so were they to say they were not down the entire period that would not be innacurate.

74° is already too high a baseline, for the room, which should about 70°, which may be accurate. Your unit says it is rack mounted, and as cpu's generate heat, the rack and its contents will be higher than that in the room. Also, the room will have both warmer and cooler locations, depending on the ducts and fans.

The timeline shows it as non-prime, which could mean far less activity, unless you've abundance of managers with BlackBerry thumb, you're running backups, or another shift/tour of duty. With their drives non spinning, computers likely generating far less heat, and their own fans being more productive.

My guess is that you went at about the limit, and lucked out. Likely not the cheapest wares.

» 1.  What is the danger zone for high temperature for a data center?

I dunno. For example, don't know layout, how cramped it may be, air flow, position of monitor etc. In days of mini/mainframe, a level of panic would set in at about 78°-80°. Days of PC more like 88°-90° room temperature. These correlate to your record and settings. Remember again that it is warmer inside the rack, and warmer inside the computer.

We'd do contingeny operations like opening of the room's doors, bringing in some large floor fans, etc. From where we sit we do not know if they did that and are in denial.

» 2.  Would an APC Netbotz give incorrect readings like this?  

I dunno, but consider it very highly unlikely. Were it to go bonkers, why would it not continue on erratically?

My guess is that there may have been some level of unreported electrical work done, and they had to shut off A/C circuit until completed.

Alernatively, I'd had cases where my complaints (temp&humid both) were discounted, then they  brought in their own monitoring and measuring devices, validating our graphs. <um> We got promises then they'd revisit processes for more steady state.

According to grapevine later on, we heard there were some members of maintenance staff who preferred to find some obscure corner to take a nap for a couple hours. Found out first by tell-tale not restoring original condition, having left some items to improve comfort on floor, some doors open, etc. Among them was next to HVAC, where person had redirected airway to keep himself warmer near rooftop.

Where environment has main shift turn their computers off when going home, another person working later would feel cooler, readjust thermostats, and block the vents to ease comfort.

Also possible, but less likely, someone may have thrown tarp over equipment as part of fire drill where there are automatic sprinklers. Or possibly, roof leaks.

Some computers came with own temp monitor, to shutdown cpu should their fans have problems, for example. It'd ne nice to have second opinion.
0
 
LVL 24

Assisted Solution

by:SunBow
SunBow earned 400 total points
ID: 40581205
Abandoned (3 Days)

> 2.  Would an APC Netbotz give incorrect readings like this?

By now your subsequent graphs ought to be answering that, being normally at a the fairly steady state that it was before the 'event'.

http://www.avtech.com/About/Articles/AVT/NA/All/-/DD-NN-AN-TN/Recommended_Computer_Room_Temperature_Humidity.htm
It is a generally agreed upon standard in the computer industry that expensive IT equipment should not be operated in a computer room or data center where the ambient room temperature has exceeded 85°F (30°C).
0

Featured Post

[Webinar] Code, Load, and Grow

Managing multiple websites, servers, applications, and security on a daily basis? Join us for a webinar on May 25th to learn how to simplify administration and management of virtual hosts for IT admins, create a secure environment, and deploy code more effectively and frequently.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Suggested Solutions

Title # Comments Views Activity
Microsoft ATA (Advance Threat Analytics) 2 65
Fraud Email 22 117
Jail break Samsung Galaxy S8 phone 3 77
internal SLA's for IT provision 6 32
Do you know what to look for when considering cloud computing? Should you hire someone or try to do it yourself? I'll be covering these questions and looking at the best options for you and your business.
Recently, Microsoft released a best-practice guide for securing Active Directory. It's a whopping 300+ pages long. Those of us tasked with securing our company’s databases and systems would, ideally, have time to devote to learning the ins and outs…
With Secure Portal Encryption, the recipient is sent a link to their email address directing them to the email laundry delivery page. From there, the recipient will be required to enter a user name and password to enter the page. Once the recipient …
The Email Laundry PDF encryption service allows companies to send confidential encrypted  emails to anybody. The PDF document can also contain attachments that are embedded in the encrypted PDF. The password is randomly generated by The Email Laundr…

738 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question