How to have redundancy aiming UPS failure?

We had a UPS failure without any advanced warning. As the result, the servers connecting to this UPS just got dead. And it was quite ugly. Question to you, How to have redundancy going against this kind of UPS failure? Shall we connect each of power supply to a different UPS or what?
The question is, the power cord coming with the servers is with a Y connectors. Each of them connects to one of the power supplies. And the other end is with only one plug which plugs to one UPS. Shall I just use two separate power cords and connect each to a separate UPS in order to accomplish the goal of redundant UPS ??
0
Castlewood
Asked:
Castlewood
4 Solutions
 
gplanaCommented:
I'm not an UPS expert but this is what I know:

- The out power (which is not the VA value, but the W value, which often is about 60% of the VA value) whould be greather than the sum of the Watts of all connected devices (o more consumption than the power that UPS can supply).

- To have redundancy you should connect 2 UPS in parallel

Hope it helps.
0
 
Don JohnstonInstructorCommented:
Question to you, How to have redundancy going against this kind of UPS failure? Shall we connect each of power supply to a different UPS or what?
On critical equipment, dual (at least) power supplies connected to separate UPS's a minimum.  Having each UPS connected to independent power source is also standard practice.
The question is, the power cord coming with the servers is with a Y connectors. Each of them connects to one of the power supplies. And the other end is with only one plug which plugs to one UPS. Shall I just use two separate power cords and connect each to a separate UPS in order to accomplish the goal of redundant UPS ??
Yes. Two power supplies, two power cords, two UPS's.
0
 
pony10usCommented:
Having each UPS connected to independent power source is also standard practice.

At the very least have each UPS on a different leg (circuit breaker)
0
 
CastlewoodAuthor Commented:
"Two power supplies, two power cords, two UPS's. "

Dell should have provided two separate power cords instead of one power cord with a Y connector.
0
 
VB ITSSpecialist ConsultantCommented:
Two separate power cords would only work if you have two power supplies - does your server have this or just the one power supply? I've never been a huge fan of Y power cables as they provide a false sense of redundancy.

Always use two power supplies for any mission critical servers and plug each PSU into separate UPS's.