Dedicated Server Room

Dear All,
What is the best way to convince senior management for them to understand why we need dedicated server room.

Currently we are building 2 a new facility where there will be a network rack with 8 switches, UPS, CCTV NVR and in future may be 1 or two servers. All the servers are currently in building 1.

Building 2 will have an admin office for 4 staff's. Management wants to commission this rack in this room.

Please help with pointing out reasons for a dedicated room. We have advised management on heat generation, dust reduction, security to the comms rack & Noise generated by these equipments.

are we missing any more points?
Please help.
Thank you
 Harry S
HardwareNetworking Hardware-OtherServer Hardware

Avatar of undefined
Last Comment
Hariharan Sivakumar

8/22/2022 - Mon
rindi

The noise from the servers and airconditioners just aren't anything for where people stay. The freezing temperatures are also no good. The carbon dioxide used to kill a possible fire would also suffocate the people in the room. Servers need to be locked away from common users, and only the admins must be allowed physical access. That means locked doors and a dedicated room
SOLUTION
Andrew Davis

Log in or sign up to see answer
Become an EE member today7-DAY FREE TRIAL
Members can start a 7-Day Free trial then enjoy unlimited access to the platform
Sign up - Free for 7 days
or
Learn why we charge membership fees
We get it - no one likes a content blocker. Take one extra minute and find out why we block content.
Not exactly the question you had in mind?
Sign up for an EE membership and get your own personalized solution. With an EE membership, you can ask unlimited troubleshooting, research, or opinion questions.
ask a question
SOLUTION
Log in to continue reading
Log In
Sign up - Free for 7 days
Get an unlimited membership to EE for less than $4 a week.
Unlimited question asking, solutions, articles and more.
D_Vante

HIPAA Security rule

45 C.F.R. § 164.310(a).

 § 164.310 Physical safeguards.
A covered entity must, in accordance
with § 164.306:
(a)(1) Standard: Facility access controls.
Implement policies and procedures
to limit physical access to its
electronic information systems and the
facility or facilities in which they are
housed, while ensuring that properly
authorized access is allowed.
(2) Implementation specifications:
Hariharan Sivakumar

ASKER
Thank you Dvante, Great information point out.
We operate from Melbourne Australia. Can you help us find out what is applicable in Australia. I will also search for the information.
Regards
Harry S
This is the best money I have ever spent. I cannot not tell you how many times these folks have saved my bacon. I learn so much from the contributors.
rwheeler23
Hariharan Sivakumar

ASKER
Thank you David Johnston, Rindi & Andrew Davis.

Management says they are only keen on a network equipment rack and they do not want us to install or migrate servers from building 1.

Our task today is to explain them why Network racks with
6 HP procurve switches, APC rack mounted UPS, Hikvision NVR

Needs a dedicated room.

Please help
Regards
Harry S
D_Vante

There is the Australian Privacy Act
Hariharan Sivakumar

ASKER
Thank you Dvante how can Australian Privacy act govern network rack installation in dedicated room?
Get an unlimited membership to EE for less than $4 a week.
Unlimited question asking, solutions, articles and more.
Hariharan Sivakumar

ASKER
Dvante what I have found out so far

AS/NZS 3084 & AS/NZS 3080 deals with building code and practice. Governs Network / IT equipment rooms.

Im looking for more information on Privacy act governing or enforcing compliance on businesses like us to have dedicated Network comms room or Server room.

Thank you.
Harry S
ASKER CERTIFIED SOLUTION
Log in to continue reading
Log In
Sign up - Free for 7 days
Get an unlimited membership to EE for less than $4 a week.
Unlimited question asking, solutions, articles and more.
Hariharan Sivakumar

ASKER
Thank you All for your comments. We will close the question and award points.

We placed below points in front of management now waiting for the decision from business.

•      These equipment’s are designed to work in a clean, temperature controlled environment, trying to keep the large space down to these temperatures is going to uncomfortable for the staff’s and expensive to run.
•      Network & server racks needs to be locked away from common users. Only the admins must be allowed physical access.
•      Protect the Network Rack devices from dust.
•      Noise level not ideal for knowledge workers. Reduced Concentration levels. Average rack noise decibel – 70 DB.
      Maintain Humidity between 35 – 40 %
•      IT team can perform maintenance task on the Network rack equipment’s anytime, without interrupting the staff’s in the room.
•      •      Space required for Network rack will be 2M X 2M.Racks to be at least 42RU 800mm X 900mm X 900mm space at front , back and sides of the racks or rack assembly as per the Australian standards AS/NZS 3084 & AS/NZS 3080.
All of the above means a locked and dedicated room.