UPS Power design

Currently, a UPS of 3KVa are connected directly to a wall socket.

We are using 220V and connect servers through a 13A power socket. Does it mean the max. UPS that I can install in 3.5Kva (assume 80% efficiency for the UPS).

Power = 220V x 13A / 0.8 = 3.5Kva

What should I construct the power supply if I need to support large power, say 4Kva or more ?

Thx
Avatar of Mal Osborne
Mal Osborne
Flag of Australia image

It is a bit more complex than that, but yeah, your math is basically correct. One thing you have forgotten however is charging current. Assume you have just had an extended outage. The UPS batteries are now depleted with just a few % left in them.  When the power is restored, you might have servers using 3KVA, however another .5KVA or so will be used to recharge the batteries, for the next couple of hours or so.

Larger UPS are generally hardwired.
Avatar of AXISHK
AXISHK

ASKER

"Larger UPS are generally hardwired. " do you mean that the UPS power is connected directly to Main supply unit, rather than plugging into the wall socket ?

Any more information about this design ?

Thx
ASKER CERTIFIED SOLUTION
Avatar of Mal Osborne
Mal Osborne
Flag of Australia image

Link to home
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
Start Free Trial
not sure how to understand " What should I construct the power supply if I need to support large power"

if you need to support a load of say 5 KVA, you need to calculate the down time it must support the load : 5KVAx 2 hour =  10 KW support batteries

you can use the calculator here :  http://www.apc.com/template/country_selection.cfm?ref_url=/tools/ups_selector/by_device.cfm?args=US/en/server
Avatar of AXISHK

ASKER

I mean for a 5Kva UPS,  I can't plug it directly to a wall power socket, correct ?

Thx
why not?  i don't see any reason
Worst case scenario, a 5000VA UPS will draw close to 30amps. 30AMP wall sockets exist, so you could use one of those.

Below is the USA version.

http://www.stayonline.com/detail.aspx?id=4790
Avatar of AXISHK

ASKER

In HK, we are using 220V. Do I need to check maxium current that the wall socket can supply ? Where can I check ?
SOLUTION
Link to home
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
Start Free Trial
SOLUTION
Link to home
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
Start Free Trial
Avatar of AXISHK

ASKER

Thx