AXISHK
asked on
UPS Power design
Currently, a UPS of 3KVa are connected directly to a wall socket.
We are using 220V and connect servers through a 13A power socket. Does it mean the max. UPS that I can install in 3.5Kva (assume 80% efficiency for the UPS).
Power = 220V x 13A / 0.8 = 3.5Kva
What should I construct the power supply if I need to support large power, say 4Kva or more ?
Thx
We are using 220V and connect servers through a 13A power socket. Does it mean the max. UPS that I can install in 3.5Kva (assume 80% efficiency for the UPS).
Power = 220V x 13A / 0.8 = 3.5Kva
What should I construct the power supply if I need to support large power, say 4Kva or more ?
Thx
ASKER
"Larger UPS are generally hardwired. " do you mean that the UPS power is connected directly to Main supply unit, rather than plugging into the wall socket ?
Any more information about this design ?
Thx
Any more information about this design ?
Thx
ASKER CERTIFIED SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
not sure how to understand " What should I construct the power supply if I need to support large power"
if you need to support a load of say 5 KVA, you need to calculate the down time it must support the load : 5KVAx 2 hour = 10 KW support batteries
you can use the calculator here : http://www.apc.com/template/country_selection.cfm?ref_url=/tools/ups_selector/by_device.cfm?args=US/en/server
if you need to support a load of say 5 KVA, you need to calculate the down time it must support the load : 5KVAx 2 hour = 10 KW support batteries
you can use the calculator here : http://www.apc.com/template/country_selection.cfm?ref_url=/tools/ups_selector/by_device.cfm?args=US/en/server
ASKER
I mean for a 5Kva UPS, I can't plug it directly to a wall power socket, correct ?
Thx
Thx
why not? i don't see any reason
Worst case scenario, a 5000VA UPS will draw close to 30amps. 30AMP wall sockets exist, so you could use one of those.
Below is the USA version.
http://www.stayonline.com/detail.aspx?id=4790
Below is the USA version.
http://www.stayonline.com/detail.aspx?id=4790
ASKER
In HK, we are using 220V. Do I need to check maxium current that the wall socket can supply ? Where can I check ?
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
ASKER
Thx
Larger UPS are generally hardwired.