I cause my own problems most times.  but I don't think  it's this time.

I took an old APC 550VA UPS that had a dead battery and wired the battery leads to a cigarette lighter plug. I wanted to make it into an inverter to get 120V in the car.  I have a couple inexpensive inverters but wanted to try this with an old UPS.  I had opened up the UPS and broke the buzzer so it's not beeping when running on the car battery.

Checking the voltage coming out of the UPS when running on the (car) battery via the cig. lighter jack, it said 90V.  (with both an old sears craftsman digital VOM and a new Harbor freight digital VOM).

I took an unmodified similar but newer APC UPS and measured that with AC power (120v) and when it was on the internal battery (around 90v like on the UPS I modified).

I plugged in some transformer bricks and USB power adapters and they put out their rated voltage (12v and 5v).

I don't have an olliliscope... is the 90v because the UPS makes a different wave rather than the sine wave from power outlets and that looks to cheap VOMs to be less than 120V?!

Thanks!
0
Comment
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
  • 3
  • 2
5 Comments
 

Accepted Solution

by:
BeGentleWithMe-INeedHelp earned 0 total points
ID: 41727930
0
 
LVL 4

Expert Comment

by:Obaid ur Rehman
ID: 41728288
When UPS is not connected to the main power and it is using battery power, the voltage of the batteries will be indicated a little low and power is being drawn out of it. When it is connected to Main, the voltage you measure are actually charging voltage, not the actual voltage of the battery. If you disconnect Main power and measure battery voltage on it's terminals, that is the correct battery voltage.

If a load is present, battery will indicate a little further low voltage as power is being drawn.
0
 

Author Comment

by:BeGentleWithMe-INeedHelp
ID: 41728293
i'm talking the voltage at the 120v receptacles when running on batteries,  not the battery voltage
0
 
LVL 4

Expert Comment

by:Obaid ur Rehman
ID: 41728304
I am having trouble understanding your question. Does it give low out put power (90V AC) on batteries instead of 120V?

APC UPSs are configured with APC Link Protocol. It may give strange behavior if not configured properly but it doesn't necessarily means the UPS is broken or faulty.
0
 

Author Closing Comment

by:BeGentleWithMe-INeedHelp
ID: 41735658
I found the answer on the web
0

Featured Post

When ransomware hits your clients, what do you do?

MSPs: Endpoint security isn’t enough to prevent ransomware.
As the impact and severity of crypto ransomware attacks has grown, Webroot has fought back, not just by building a next-gen endpoint solution capable of preventing ransomware attacks but also by being a thought leader.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

PRTG Network Monitor lets you monitor your bandwidth usage, so you know who is using up your bandwidth, and what they're using it for.
As cyber crime continues to grow in both numbers and sophistication, a troubling trend of optimization has emerged over the last year.
In this video we outline the Physical Segments view of NetCrunch network monitor. By following this brief how-to video, you will be able to learn how NetCrunch visualizes your network, how granular is the information collected, as well as where to f…
NetCrunch network monitor is a highly extensive platform for network monitoring and alert generation. In this video you'll see a live demo of NetCrunch with most notable features explained in a walk-through manner. You'll also get to know the philos…
Suggested Courses

660 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question