What wall mount rack make/model do you
recommend for the below equipment ?

 1. 48port patch panel
 2. 48port patch panel cable management (i.e. http://neatpatch.com)
 3. Cisco 48port POE switch
 4. rack mounted 5 minute UPS for switch
         --> do NOT know weight, might be TOO heavy for rack ?
0
Comment
Question by:finance_teacher
[X]
Welcome to Experts Exchange

Add your voice to the tech community where 5M+ people just like you are talking about what matters.

  • Help others & share knowledge
  • Earn cash & points
  • Learn & ask questions
3 Comments
 
LVL 39

Assisted Solution

by:Aaron Tomosky
Aaron Tomosky earned 125 total points
ID: 41761928
Chatsworth is my goto for wall mount racks. Just make sure it's deep enough for all your gear. Yes the ups might be too heavy.
http://www.chatsworth.com/products/wall-mount-systems/wall-mount-open-systems/
0
 
LVL 43

Accepted Solution

by:
Davis McCarn earned 250 total points
ID: 41762283
Since each POE port can draw up to an additional 30 watts, you really need to check the POE devices to know what the power requirements may be and you may even need to add a secondary power supply to the Cisco.
Read this:
http://www.cisco.com/c/en/us/products/collateral/switches/catalyst-3750-x-series-switches/white_paper_c11-663717.html

And, no matter what, please take the time to mark the remote ports and every cable in the patch panel!  Having to use a testing device to find a wire later is a real PITA.

Eaton makes extremely good UPS' and this guy looks like it will handle things (do your math from above first); but, at 55 pounds, you would want that wallmount attached to a sheet of plywood which was also screwed into the studs: https://www.cdw.com/shop/products/Eaton-9130-UPS-1500VA-1350W-120V-2U-Rack-Mount-Special-Price/1587110.aspx
0
 
LVL 37

Assisted Solution

by:ArneLovius
ArneLovius earned 125 total points
ID: 41762386
I would NOT put a rack mounted UPS in a wall mounted rack, especially if you are using full depth switches. It;s not just the load capacity of the rack, its the load capacity of the wall and the fixings, the deeper the rack the bigger the lever...

and I have seen the aftermath of somebody putting a UPS on top of a wall mounted comms cabinet, it pulled the fixings out of the wall and ripped the network cables out, not a pretty sight, and very expensive to remediate, had to recable...

I would either use a floor standing rack (doesn't have to be full height), or have the UPS external to the rack
0

Featured Post

How our DevOps Teams Maximize Uptime

Our Dev teams are like yours. They’re continually cranking out code for new features/bugs fixes, testing, deploying, responding to production monitoring events and more. It’s complex. So, we thought you’d like to see what’s working for us. Read the use case whitepaper.

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

Transparency shows that a company is the kind of business that it wants people to think it is.
Data center, now-a-days, is referred as the home of all the advanced technologies. In-fact, most of the businesses are now establishing their entire organizational structure around the IT capabilities.
After creating this article (http://www.experts-exchange.com/articles/23699/Setup-Mikrotik-routers-with-OSPF.html), I decided to make a video (no audio) to show you how to configure the routers and run some trace routes and pings between the 7 sites…
Get a first impression of how PRTG looks and learn how it works.   This video is a short introduction to PRTG, as an initial overview or as a quick start for new PRTG users.

751 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question