What should I need to check on APC Smart UPS as a Preventive maintenance ?

Thx
0
Comment
Question by:AXISHK
  • 4
  • 2
  • 2
  • +3
13 Comments
 
LVL 9

Expert Comment

by:Tomas Valenta
ID: 41804334
The most important is battery condition (capacity) and for your information how long will this UPS serve your equipments before it shut down.
0
 

Author Comment

by:AXISHK
ID: 41804336
There is a "test" button on the UPS, should I press it to check for potential problem ?

Thx
0
 
LVL 9

Assisted Solution

by:Tomas Valenta
Tomas Valenta earned 89 total points
ID: 41804372
If the UPS has management adapter you can configure tests in web interface and receive results by e-mail. Test button on UPS make a test but no result visible.
0
Comprehensive Backup Solutions for Microsoft

Acronis protects the complete Microsoft technology stack: Windows Server, Windows PC, laptop and Surface data; Microsoft business applications; Microsoft Hyper-V; Azure VMs; Microsoft Windows Server 2016; Microsoft Exchange 2016 and SQL Server 2016.

 
LVL 93

Accepted Solution

by:
John Hurst earned 150 total points
ID: 41804652
There is a software application that came with the UPS that you can install. I have done that on my APC UPS.

All you really need to know is the battery health and age. At 3 or 4 years old, it is time to consider replacing the batteries.
0
 
LVL 4

Assisted Solution

by:Obaid ur Rehman
Obaid ur Rehman earned 87 total points
ID: 41804884
If you are looking for suggestions for Periodic Preventive Maintenance, there's very less you can do but matters.

1- Checking Battery health (from the UPS software (PowerChute) or by just observing). PowerChute also offers some other tools for event logging and limited configuration (depends on UPS model)
2- You can use a blower to clean inside.
3- If your UPS is showing abnormal behavior, most probably there's configuration issue. Note: most problems can be resolved using APC cable (black one) and Telnet.
Over the time when battery gets weaker, the software changes the battery constant (different for different models). In most cases, the UPS will report it with Battery LED. If it doesn't and the backup time is greatly reduced, most probably the battery is close to death. The "test" button actually simulates power failure and calculates the available runtime of the battery, it then updates the battery constant in the configuration. It is by default set to 14 days. So pressing it would not help.

You can also use APC UPS Daemon as an alternative to PowerChute.

Hope that helps!
0
 
LVL 28

Assisted Solution

by:serialband
serialband earned 87 total points
ID: 41805164
In addition to the above:

Lead Acid Gel Cells last up to 5 years without any deep cycle drains, but you probably need to replace them at 3-4 years if you want longer uptime from them, even if the batteries still work.  They can do about 8 full cycle drains before you have to replace them, but you may want to replace them even before that time, depending on your uptime needs. One company I service has to replace the batteries every 2 years, because of all the outages they have.
0
 
LVL 25

Assisted Solution

by:Dr. Klahn
Dr. Klahn earned 87 total points
ID: 41805736
The solution I believe in for testing a UPS is to unplug it at the wall, and then see if the actual runtime meets expectations.  If not, it's time for a new battery or a larger capacity UPS.
0
 
LVL 93

Expert Comment

by:John Hurst
ID: 41805739
That will work, but the UPS software will tell you the same thing.

Lasting time depends on load. My UPS will start shutting things down in 15 minutes (lots of capacity left), but with only a network load (computers off or laptop on battery), it is good for a couple of hours.
0
 
LVL 25

Expert Comment

by:Dr. Klahn
ID: 41805743
That will work, but the UPS software will tell you the same thing.

In my own experience, this is not always true.  The UPS software makes the potentially invalid assumption that everything in the UPS is normal.  As examples, if a wire has corroded or an output MOSFET has failed, the only way to discover that is to exercise the UPS.
0
 
LVL 93

Expert Comment

by:John Hurst
ID: 41805745
It normally works for me and for my clients. I do not keep these in damp environments, and short of an outright failure, they do not corrode inside.
0
 

Author Closing Comment

by:AXISHK
ID: 41805774
Thx
0
 
LVL 93

Expert Comment

by:John Hurst
ID: 41805781
You are very welcome and I was happy to help.
0
 
LVL 28

Expert Comment

by:serialband
ID: 41805793
Exercising the UPS for a full deep cycle shortens the time for the next deep cycle.  Don't do it.

It's best to just keep track and replace the batteries on a proper fixed schedule, based on how many deep cycles you've had and how many years you've had them.  Having dealt with a location that has quarterly outages that last 2 hours or more, I've had experience with UPS battery life.  At 1 cycle per quarter, 8 cycles means just about 2 years of battery life before replacement is definitely needed at this site.

That's in line with the deep cycle life of full house/full business battery backups for Solar Panels for the same amount of cycles.  They basically told me the same thing that I found from experience when I got a quote for a commercial location.  If you don't ever deep cycle your lead acid batteries, they can last up to about 5 years, but if you want to keep the same uptime, 4 years is when you swap them.

The sliding scale is 8 full deep cycles or about 4 years, whichever comes first.  That basically means that each full deep cycle shortens the life by about 6 months.  Powerchute can really only tell you charge levels by checking the voltage and doesn't really keep track of the cycling.  It's only really good for telling you if the UPS failed earlier than expected, because one of the cells failed sooner than expected to generate a lower voltage.
0

Featured Post

Complete VMware vSphere® ESX(i) & Hyper-V Backup

Capture your entire system, including the host, with patented disk imaging integrated with VMware VADP / Microsoft VSS and RCT. RTOs is as low as 15 seconds with Acronis Active Restore™. You can enjoy unlimited P2V/V2V migrations from any source (even from a different hypervisor)

Question has a verified solution.

If you are experiencing a similar issue, please ask a related question

I use more than 1 computer in my office for various reasons. Multiple keyboards and mice take up more than just extra space, they make working a little more complicated. Using one mouse and keyboard for all of my computers makes life easier. This co…
This is about my first experience with programming Arduino.
This Micro Tutorial will teach you how to censor certain areas of your screen. The example in this video will show a little boy's face being blurred. This will be demonstrated using Adobe Premiere Pro CS6.
This video shows how to quickly and easily add an email signature for all users on Exchange 2016. The resulting signature is applied on a server level by Exchange Online. The email signature template has been downloaded from: www.mail-signatures…

777 members asked questions and received personalized solutions in the past 7 days.

Join the community of 500,000 technology professionals and ask your questions.

Join & Ask a Question