UPS APC Smart-UPS SRT 5000VA
In the specs saying :
APC Smart-UPS SRT 5000VA RM 208V to 120V 2U Step-Down Transformer
Does that mean it has 208V input and 120V output. Or I can plug it in either into 120V or 208V?
Do I need to have 208V 30Amp plug for this?
APC Smart-UPS SRT 5000VA RM 208V to 120V 2U Step-Down Transformer
Does that mean it has 208V input and 120V output. Or I can plug it in either into 120V or 208V?
Do I need to have 208V 30Amp plug for this?
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
208 Volts is NOT 240 Volts, rather it is normally 3 phase voltage. Most homes would not have such outlets.
Check with APC to see if this is what you really have as normally it would have to be wired in.
I am not sure why it would be labelled this way except that it may be a special unit.
Check with APC to see if this is what you really have as normally it would have to be wired in.
I am not sure why it would be labelled this way except that it may be a special unit.
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
ASKER
Perfect thanks dhsindy! Follow-up q.-
Yes this is a commercial building, but.. we may not have 208V in there.
If they only have NEMA 5-30R. What are my options for the UPS and how many wall receptacles and circuits will I need?
Yes this is a commercial building, but.. we may not have 208V in there.
If they only have NEMA 5-30R. What are my options for the UPS and how many wall receptacles and circuits will I need?
I have not seen a 208 Volt outlet. These devices are wired in so you need to contact an electrician for wiring.
Can you return the unit for a more standard unit?
Can you return the unit for a more standard unit?
ASKER
Nah, very common. APC has L6-30P. Works with 208V or 240V.
Standard 240 Volt outlets are easy to install and safe to use. Get an electrician to put one where you need it. Easy. I have one in my basement
ASKER
I think we derailed from the q. IF I cannot get L6-30R installed. Only NEMA 5-30R.
Is there another UPS that can hold the same load?
Is there another UPS that can hold the same load?
APC have lots of units for a variety of loads. Just pick one. Big units will likely want a 240 Volt input (more efficient)
ASKER
Right... so my question is. Which units do I need to replace that unit. IF I cannot get 208V in that building.
Here is the replacement unit using 230 Volts IN (same as 240 Volts)
http://www.apc.com/shop/id/en/products/APC-Smart-UPS-5000VA-230V-Rackmount-Tower/P-SUA5000RMI5U
Also there was a 208 Volt unit next in the list - different unit.
http://www.apc.com/shop/id/en/products/APC-Smart-UPS-5000VA-230V-Rackmount-Tower/P-SUA5000RMI5U
Also there was a 208 Volt unit next in the list - different unit.
ASKER
How about 120V? NEMA 5-30R
That would probably work but it would take twice the current to run it as a 240 Volt unit.
For that kind of unit stick with 240 Volts as you will need an electrician anyway
For that kind of unit stick with 240 Volts as you will need an electrician anyway
How much output do you actually need? With a 240V input you'll be able to get about double the output power of something with a 120V input.
5000 VA at 120 Volts is a 50 Amp circuit. 25 Amps for 240 Volts
ASKER
Thanks CompSolv. Agreed. So that mean I would need two smaller 120V units to replace one 240V.
Which units would that be?
Which units would that be?
Start with the link I provided and search again for 2500 VA units. See if they are available in 120 Volt input. Still, you would need a 25 Amp circuit so special wiring in any event.
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
Isn't it considered a bad practice to use 2 legs of a 3-phase system unless you can balance it out elsewhere?
Isn't it considered a bad practice to use 2 legs of a 3-phase system
Yes. Tiras25 - use standard 240 Volt units. APC has proper units for you and no need to get 208 Volt units.
Also for the power you need (you say) use a 240 Volt system. An electrician can easily put an outlet (or two) in for you.
Yes. Tiras25 - use standard 240 Volt units. APC has proper units for you and no need to get 208 Volt units.
Also for the power you need (you say) use a 240 Volt system. An electrician can easily put an outlet (or two) in for you.
ASKER CERTIFIED SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
ASKER
SRT5KRMXLT-5KTF SCHNEIDER ELECTRIC APC Smart-UPS SRT 5000VA
RM 208V to 120V 2U Step-Down Transformer
I wonder if I don't have 208V wall receptacle L6-30R. What are my options? Buying different UPS models?