Can I independently power a 120V line if either of 2 other lines are ON?
I've got two 120V lines coming from breaker panel. Circuit A is power to the outdoor flood lights, Circuit B is power to the garage door opener, which powers its own lights. I want to install a 3rd set of lights under the eaves in front of the garage that will be turned on if either the outdoor flood lights are on or the garage door opener lights are on.
The intent is to get plenty of light in front of the garage when the door is opened or to provide as much light as possible if the flood lights are on without the two existing circuits bleeding over into each other and all the lights coming on.
ASKER
@David
The concept isn't very tough. I've done a lot of wiring over the years but this is the first time that this has come up. I seems like a normal thing to want to do so I'm wondering why I can't find readily available solutions.
The concept isn't very tough. I've done a lot of wiring over the years but this is the first time that this has come up. I seems like a normal thing to want to do so I'm wondering why I can't find readily available solutions.
Buy two X-10 control modules that signal when they have power. Attach one to the existing lights, attach the other to the garage door opener's light socket.
Drive the new set of lights with an X-10 receiver on the same channel as the two control modules.
Drive the new set of lights with an X-10 receiver on the same channel as the two control modules.
The issue is first the flood lights are likely operated by a motion sensor feeding it out to the other would get complicated.
Do the flood lights include an external outlet?
The straight forward your door opener circuit is a 20Amp circuit extending it pre-garage door opener should be enough and all you need for the additional lights is a motion sensor.
Often, extending the power from the flood lights which are already at the wall.
You might want to add lights to the garage door triggered illumination and half along the flood lights route to achieve the best of both worlds.
Do the flood lights include an external outlet?
The straight forward your door opener circuit is a 20Amp circuit extending it pre-garage door opener should be enough and all you need for the additional lights is a motion sensor.
Often, extending the power from the flood lights which are already at the wall.
You might want to add lights to the garage door triggered illumination and half along the flood lights route to achieve the best of both worlds.
ASKER
@arnold
I'm looking to install some under-eave lighting to augment the existing lighting. There are woods directly behind the garage and a biker bar is the first thing on the other side of the woods. A couple of LED ceiling lights will light up the garage entrance just fine. If controllable by both circuits they will also help light up everything when the floods are on. The lights are cheap enough that I could install 4, connecting 2 to each circuit, but that winds up looking quite odd.
I'm looking to install some under-eave lighting to augment the existing lighting. There are woods directly behind the garage and a biker bar is the first thing on the other side of the woods. A couple of LED ceiling lights will light up the garage entrance just fine. If controllable by both circuits they will also help light up everything when the floods are on. The lights are cheap enough that I could install 4, connecting 2 to each circuit, but that winds up looking quite odd.
Not sure of the arrangement, you could use a similar mechanism like car door openers
to activate/deactivate the light on/off event
The power on/off based on garage door activator is fairly straight forward as it has/includes the light that are turned on and off when the door it opened and closed.
The floods rely on a motion sensor I suspect, and that commonly means the floods have to have an outlet controlled by the motion sensor.
using relays that are remotely activated
ie. garage door opens, the relay connected there triggers the event ..
garage door close...
Distances and things are what come to mind
See examples with rfid and relays.
https://www.amazon.com/rf-relay/s?k=rf+relay
to activate/deactivate the light on/off event
The power on/off based on garage door activator is fairly straight forward as it has/includes the light that are turned on and off when the door it opened and closed.
The floods rely on a motion sensor I suspect, and that commonly means the floods have to have an outlet controlled by the motion sensor.
using relays that are remotely activated
ie. garage door opens, the relay connected there triggers the event ..
garage door close...
Distances and things are what come to mind
See examples with rfid and relays.
https://www.amazon.com/rf-relay/s?k=rf+relay
ASKER
A feed like this will result in 240 when both are on.
The relay is not the issue, you want two different actuators to turn it on and be on if both are on.
Your post garage door openner is still 120V feed
you could have a step down feed from the 120V to 12 DC to go towards the relay as you depict that can tolerate a draw of 12-24V on the switching side @15ma.
You have two triggering options
Garadoor Flood lights actuator
0 0 0
0 1 1
1 0 1
1 1 1
https://www.amazon.com/Electronics-Salon-SPST-NO-Module-Control-Voltage/dp/B01B60RZPA/ref=sr_1_1_sspa?dchild=1&keywords=24v+120v+relay&qid=1632774206&sr=8-1-spons&psc=1&spLa=ZW5jcnlwdGVkUXVhbGlmaWVyPUExS0NIWEczQTVJQ0QmZW5jcnlwdGVkSWQ9QTA1NjE5MzkzNzJLWE43MUJHQjZMJmVuY3J5cHRlZEFkSWQ9QTAwMjExNTMyUkJQUVdZVEdHSEhaJndpZGdldE5hbWU9c3BfYXRmJmFjdGlvbj1jbGlja1JlZGlyZWN0JmRvTm90TG9nQ2xpY2s9dHJ1ZQ==
The relay is not the issue, you want two different actuators to turn it on and be on if both are on.
Your post garage door openner is still 120V feed
you could have a step down feed from the 120V to 12 DC to go towards the relay as you depict that can tolerate a draw of 12-24V on the switching side @15ma.
You have two triggering options
Garadoor Flood lights actuator
0 0 0
0 1 1
1 0 1
1 1 1
https://www.amazon.com/Electronics-Salon-SPST-NO-Module-Control-Voltage/dp/B01B60RZPA/ref=sr_1_1_sspa?dchild=1&keywords=24v+120v+relay&qid=1632774206&sr=8-1-spons&psc=1&spLa=ZW5jcnlwdGVkUXVhbGlmaWVyPUExS0NIWEczQTVJQ0QmZW5jcnlwdGVkSWQ9QTA1NjE5MzkzNzJLWE43MUJHQjZMJmVuY3J5cHRlZEFkSWQ9QTAwMjExNTMyUkJQUVdZVEdHSEhaJndpZGdldE5hbWU9c3BfYXRmJmFjdGlvbj1jbGlja1JlZGlyZWN0JmRvTm90TG9nQ2xpY2s9dHJ1ZQ==
In a way what you are looking for is a switch that mimics the functionality of a power backup switch.
One position and primary is post garage door feed, if there is no power, it auto switches to the other position.
This way when both are on, only the primary circuit will be active.
Power from garage door ====>*
* <==feed to set of lights
Power from flood light source ====>>*
The swing of connector is controlled by power on the primary designated live.
I.e. Garage door open, relay triggers closes that circuit, garage door closed, the relay falls back closing the other circuit without regard on whether it is powered or not.
One position and primary is post garage door feed, if there is no power, it auto switches to the other position.
This way when both are on, only the primary circuit will be active.
Power from garage door ====>*
* <==feed to set of lights
Power from flood light source ====>>*
The swing of connector is controlled by power on the primary designated live.
I.e. Garage door open, relay triggers closes that circuit, garage door closed, the relay falls back closing the other circuit without regard on whether it is powered or not.
ASKER CERTIFIED SOLUTION
membership
This solution is only available to members.
To access this solution, you must be a member of Experts Exchange.
To correct the above image for accuracy, they share a neutral line, Black.
of you need to have a ground (green) to avoid overloads.....
of you need to have a ground (green) to avoid overloads.....
ASKER
@Arnold.
The device I'm looking for (the blue box) was a simple flip-flop back when most parts were mechanical. 240V won't happen since the flip-flop will connect the output to either input but not both simultaneously.
Both of the relays you linked require a low-voltage control circuit. I want to avoid that. (Actually bought one of them, but decided to go another direction.)
But the power backup switch sounds interesting. I hadn't consider that until now. Gonna investigate! :)
The device I'm looking for (the blue box) was a simple flip-flop back when most parts were mechanical. 240V won't happen since the flip-flop will connect the output to either input but not both simultaneously.
Both of the relays you linked require a low-voltage control circuit. I want to avoid that. (Actually bought one of them, but decided to go another direction.)
But the power backup switch sounds interesting. I hadn't consider that until now. Gonna investigate! :)
The one I linked to, zoom in on the spec, it looks like the coil is a 120 actuator.
The max rating on no nc and common is 30Amp @240
If you feed 120 120 cones out
If you have a 120V relay with a 12 volt trigger, you could use a ac to DC adapter that has 12 volt. Usually it needs to draw 25 milliamperes through the solenoid to switch from normally closed position to the normally open circuit.
The max rating on no nc and common is 30Amp @240
If you feed 120 120 cones out
If you have a 120V relay with a 12 volt trigger, you could use a ac to DC adapter that has 12 volt. Usually it needs to draw 25 milliamperes through the solenoid to switch from normally closed position to the normally open circuit.
ASKER
I did. :)
I took 30A/14V to mean a 14V control circuit.
I took 30A/14V to mean a 14V control circuit.
Not sure I know where you saw this,
Description of item a lamp on the circuit ...
Description of item a lamp on the circuit ...
Tnisesm 2PCS Power Relay AC120V Coil, 30A SPDT(1NO 1NC) 120 VAC w
ASKER
https://www.amazon.com/Tnisesm-Mounting-Connect-Terminals-NT90-AC120V-10X/dp/B087G6D24G/ref=sr_1_1_sspa?dchild=1&keywords=120v+relay&qid=1632791362&sr=8-1-spons&psc=1&spLa=ZW5jcnlwdGVkUXVhbGlmaWVyPUExTVdHRFU5TkFKNEU4JmVuY3J5cHRlZElkPUEwMDM3ODcyUEVaMk5BWlUzMjc2JmVuY3J5cHRlZEFkSWQ9QTA3MTg0NjEzR1hVS05BODc4MDhVJndpZGdldE5hbWU9c3BfYXRmJmFjdGlvbj1jbGlja1JlZGlyZWN0JmRvTm90TG9nQ2xpY2s9dHJ1ZQ==
Zoom over the unit. 3rd row of text on the right.
Zoom over the unit. 3rd row of text on the right.
I think you might be misreading the notation.
50/60 HZ 30A/240
30A/14V DC
-120vAC
I think the first two describe the max wattage through the nc/no comm terminals.
That 30A/14v make o sense. Usually, actuator circuit provide voltage and ii alike ape rage need to actuate.
30Amp from a 14 V source has more sense to be a max rating for flow, versus for the actuator circuit info.
Some of the exchanges with the seller, has a clarification that this relay is a 120v actuator
The relay, circuit, document/usage I gt clarify.
50/60 HZ 30A/240
30A/14V DC
-120vAC
I think the first two describe the max wattage through the nc/no comm terminals.
That 30A/14v make o sense. Usually, actuator circuit provide voltage and ii alike ape rage need to actuate.
30Amp from a 14 V source has more sense to be a max rating for flow, versus for the actuator circuit info.
Some of the exchanges with the seller, has a clarification that this relay is a 120v actuator
The relay, circuit, document/usage I gt clarify.
Now that the option is available, it is the means to achieve.
https://www.digikey.com/en/products/detail/picker-components/PTRA-1C-120S-T5-X/12318142?utm_adgroup=&utm_source=bing&utm_medium=cpc&utm_campaign=Shopping_DK%2BSupplier_Other&utm_term=&utm_content=&utm_id=bi_cmp-384720322_adg-1306220140326442_ad-81638827568289_pla-4585238372516895_dev-c_ext-_prd-12318142&msclkid=9d0e2beb80d014f430234ab8dcbe198a
The actuator seems to be an AC120 with 16.5ma accross the circuit to activate.
Connecting a USB charger might be enough to generate a 16.5ma leak when the whatever you connect to the NO terminal is turned on, and ...
The main thrust of your need is a relay that can handle the 120V and the amperage through the relay.30/40AMP is a bit much based on your description.
But I think you are cloer o the electrical side. the placement of the wires or the connecting .....
The location from which you want to extend the lights. does it have its own power source?
i.e. a though of a remote RFID type of activator.
Similr to a car door opener. press one on, press two off using relays to generate a pulse ....
https://www.digikey.com/en/products/detail/picker-components/PTRA-1C-120S-T5-X/12318142?utm_adgroup=&utm_source=bing&utm_medium=cpc&utm_campaign=Shopping_DK%2BSupplier_Other&utm_term=&utm_content=&utm_id=bi_cmp-384720322_adg-1306220140326442_ad-81638827568289_pla-4585238372516895_dev-c_ext-_prd-12318142&msclkid=9d0e2beb80d014f430234ab8dcbe198a
The actuator seems to be an AC120 with 16.5ma accross the circuit to activate.
Connecting a USB charger might be enough to generate a 16.5ma leak when the whatever you connect to the NO terminal is turned on, and ...
The main thrust of your need is a relay that can handle the 120V and the amperage through the relay.30/40AMP is a bit much based on your description.
But I think you are cloer o the electrical side. the placement of the wires or the connecting .....
The location from which you want to extend the lights. does it have its own power source?
i.e. a though of a remote RFID type of activator.
Similr to a car door opener. press one on, press two off using relays to generate a pulse ....
ASKER
- The location from which you want to extend the lights. does it have its own power source?i.e. a though of a remote RFID type of activator.
Not really. Presently, there's only the switched 120V lines.
Oh, so you have to extend the wires from the garage/flood light to the area where you want to add them.
Does the flood light have an outlet ?
See whether some garage openers might have a lower output i.e. a 48/24 volt
you could test the relays without the need to run wires...as a test with one bulb..
getting the relays and testing their functionality before..
running the wires, have to go under driveway to the other side?
Does the flood light have an outlet ?
See whether some garage openers might have a lower output i.e. a 48/24 volt
you could test the relays without the need to run wires...as a test with one bulb..
getting the relays and testing their functionality before..
running the wires, have to go under driveway to the other side?
ASKER
Think I figured this out. A 120V SPDT relay should do the trick.
With both switches off, the relay activates the top circuit. When the top switch is turned on, the lights (load) are turned on.
When the bottom switch is turned on, the relay changes to the other input and again, the light is turned on.
When both switches are on, the voltage from the top switch terminates and the bottom circuit powers the load.
The Neutral does not connect to the hot at the bottom of the picture. :) And the thin blue light represents the alternate connection.
The relay draws power only when the lower switch is on (and the lights).
It might take me a little while to actually get in the attic and wire all this up, but I feel good about it!
Thanks for helping talk me through this!
With both switches off, the relay activates the top circuit. When the top switch is turned on, the lights (load) are turned on.
When the bottom switch is turned on, the relay changes to the other input and again, the light is turned on.
When both switches are on, the voltage from the top switch terminates and the bottom circuit powers the load.
The Neutral does not connect to the hot at the bottom of the picture. :) And the thin blue light represents the alternate connection.
The relay draws power only when the lower switch is on (and the lights).
It might take me a little while to actually get in the attic and wire all this up, but I feel good about it!
Thanks for helping talk me through this!
I think That is what my picture reflects.
Personally, I would have the relay in an accessible location, on the outside in a weather proof box for easy replacement should the relay blow for any reason..
Personally, I would have the relay in an accessible location, on the outside in a weather proof box for easy replacement should the relay blow for any reason..
ASKER
That's a good thought.
Both lines are in the attic over the garage, about 15 feet apart, and the attic access only a few feet away. I was thinking of putting it in the attic. Now I'm thinking you're right and next to the switch that's in the garage is better. I'll still have to crawl through the attic to wire it up, but if I do it right any additional maintenance will be at standard wall switch height.
Thanks again!
Kent
Both lines are in the attic over the garage, about 15 feet apart, and the attic access only a few feet away. I was thinking of putting it in the attic. Now I'm thinking you're right and next to the switch that's in the garage is better. I'll still have to crawl through the attic to wire it up, but if I do it right any additional maintenance will be at standard wall switch height.
Thanks again!
Kent
To shield the relay you might want to put a breaker (10A) after the relay to feed out the power to the outdoor lights.
sw1
or circuit powers relay that applies power to new set of lights
sw2